Hi Everyone

I would be glad if you could clarify this for me:

For a Load Estimate Survey whereby 95% is single phase, the Load Estimate is 90 KVA (Single Phase). However, the power supply is three phase 4 wire system.

To calculate the current per phase, the 90 kVA is divided by three i.e. 30 kVA per phase. Hence, current per phase is (30 x 1000/230) = 130 A/ph.

Hence, the 90 kVA single phase is equal to 90 kVA three phase??? This is where I'm confused.

In addition, to undertake a load estimate survey, which is better to workout all the currents or use the kW or kVA ratings with Utilisation factor & simultaneity factor.

Thanks in advance.
 
a 90kVA 3 phase supply will give you approx 30kVA per phase assuming the loads are balanced across the 3 phases. it would be wise to allow 20 -25% additional capacity to allow for some imbalance.
 
No, its 90 kVA Single Phase Load Estimate. Hence, if the power supply is three phase. Then, if the load is properly balanced for the three phase, the load per phase will be 30 kVA. Am I right?

Hence, I'm confused that 90 kVA Single Phase Load is equal to 90 kVA Three Phase Load.
 
Sorry David, I'll try to explain more clearly.

The total estimated single phase loads for a building is approx. 90 kVA i.e. all the equipment are single phase (socket-outlets, pumps and lighting).

However, the building has a three phase power (4 wires) supply from the utility.

If the single phase loads (90 kVA) are distributed equally over the three phase power, then the apparent power per phase is 30 kVA & the total three phase power is 90 kVA. Is this right?
 

Reply to Single Phase Load Estimate to Three Phase Power Supply in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I have a single phase stainless steel pasteuriser that has two control boxes attached to it. One box houses the control for the electronics and...
Replies
2
Views
686
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
2K
Hello, I'm new to this forum, we are in the process of converting into 12 flats all electric, no gas incl. heating, showers etc. An electrician...
Replies
10
Views
2K
Hello everyone! I have a question regarding the electricity supply and the maximum demand. One energy utility supplies an 18 kVA maximum...
Replies
10
Views
2K
(Thought I'd already poost this Q, but I cant see it, so I'll try again) We have some work going on in one of our buildings atm. On of the chaps...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock