Hi All,

I'm after a little help/advise from anyone who has any knownledge or experience in a single to 3-phase inverters.

My scenario:
We're in the final process of finishing a care home rewire, they have a 3-phase lift being installed. Everything's in place and been ran etc...

UK power networks has just given the owner a quote of over 100k to upgrade the current supply to a 3-phase supply to accommodate the 3-phase lift.

Has anyone ever fitted a 3-phase inverter? The installation currently has a 100amp supply but the loading is minimal. The lift is 31.7amps (37.8amps start up). Can I supply a 3-phase inverter with a 6mm 40amp MCB from my single phase and then supply the lift that way.

Has anyone ever installed one before? Recommendations or advise is much appreciated.
 
The biggest 1-3 phase inverters I use top out at 2.2kW, you're talking ten times that size. Plus, supplying 40A of 3-ph startup off a single line is going to fully use that 100A supply, then some more.

Bottom line, if your client wants a 20kW lift motor, they need to stump up for 3 phase incomers.
 
A standard motor inverter would not work anyway due to the fact you are not just feeding a motor, you would be feeding controls, lighting, etc.
Only option would be a rotary converter for this type of application, but even then I do not think the supply you have available is big enough. May be worth investigating though, as UKPN may be able to increase the size of the existing single phase supply for a lot less than £100k
https://www.simplypowersupply.com/pdf/mtrt.pdf
 
Didn't he say 40A was the start-up current ?
Which is more like 10KW
Where did 22kw come from ?

22kW was off my head with no working. Looked it up and an 18kW 415V motor at 0.8pf pulls ~32A FLC, as stated in the OP. To power that same 18kW off a single phase supply is 97A before conversion losses! I don't know where he got 37.8A startup from, a heavy traction lift motor is more likely to pull 100+ at startup.
 
Good planning on the designers/builders/lift owners parts of going ahead without checking the feasibility of 3 phase first...

What is the expected usage of the lift? i.e. frequency of use, weight in it etc?
 
Who thought it would be a good idea to design a 3 phase lift into a single phase house? Do they not do single phase lifts?
 
The lift is only small, and is literally going from ground to first. I've worked in one of their care homes before and the lift which was installed there was literally supplied via a 13amp plug top.

Apparently this specific lift will only come as 3-phase.
All the carriage lights and shaft lighting is supplied separately by a seperate DB situated in the corridor cupboard. Looking at the Lift document it says total running current 26.5 amps and total starting current 37.1 amps.

I was under the impression this was across phases so running current roughly 9 amps per phase, and starting current 13amps per phase.
 
I've just attached a screen shot of some specs on the drawings

IMG_8337.PNG
 
Somebody better speak to the Lift installation company before any more plans are made I doubt they will accept an inverter supply.

The lift will form part of the Fire Escape route, it will have to be bullet proof.

Only if it is designed to be an evacuation lift, if it’s just a normal lift then it won’t
 
Will it? Every block of flats I've ever done the lift is grounded in the event of a fire.

It's not a block of flats with able bodied people in it.

A true Fire escape lift is isolated from the main building and the power supply is run in a route so as not to be affected by Fire.

Even if the O.P lift is not a true Fire escape lift, it may well form part of the Fire escape strategy if Care home residents are above ground floor level.
 
It is correct that a lift for general use could be incorporated into an escape plan in an emergency situation after a risk assessment and a controlled strategic plan but generally this would be considered a high risk policy. Lifts which have been put in place as part of an escape route are subject to strict legal requirements and are generally only considered where vertical footfall is not free flowing such as a hospital where mobility may be restricted.
 
The motor is rated at under 12kW.
You can use a 1ph - 3ph VFD to control just a 3ph motor. The existing controls would be wired to the VFD controls, fairly simple if you understand the way the lift works and safety requirements etc.
But will the lift company want/know how to redesign their lift for a one off project?
No.
 

Reply to Single to 3 phase converter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Wallbox Fuse Box Lite Single Phase has anyone used one of these? I've installed one feeding a Pulsar Max, the Pulsar Max is set to 32Amp max. The...
Replies
0
Views
219
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi, As a DIYer I`ve quite a bit of wiring up domestic house single phase experience but no 3 phase experience. So I have been offered a two post...
Replies
7
Views
2K
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
954
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock