Discuss Site Temps earthing question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
1
Hi
Currently on a job at a hospital where we are installing temporary site supplies to canteen toilet block and office.
The supply is Tncs from hospital but the hospital electrician and contractor doesn’t want us to install earth rods in case of services below ground and they’re not prepared to scan ground.
Hospital electrician says we can use PME supply as long as it’s on RCD but surely this isn’t correct as if a broken PEN conductor will make all cabins live potentially and rcd won’t pick this up?
Also what other option do we have if can’t use pme and they don’t want TT. Surely under regs it has to be TT and there’s no arguing?

Thanks
 
Are you sure it's TNCS? I'd have thought that's unusual for a hospital, they normally have pretty big supplies if not 11kV incoming which would all be TNS.

But either way it will have earth rods for the backup generatir, a lightning protection system and other bonded metalwork buried in the ground. All this will add up to quite a nice earth electrode to keep things safe if a PEN fault occurs.
 

Reply to Site Temps earthing question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
Replies
19
Views
3K
Hello, not sure if this is allowed but here goes, I was recently staying on a caravan park along with many others, (touring caravan not static)...
Replies
6
Views
2K
I’ve had a shipping container delivered to my building site for use as storage/utility room/worker toilet. One side is insulated as it was...
Replies
9
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock