Discuss sma overvoltage in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

yes it is a 3600tl-20 not a 21 which i gather would stop this problem
That's well outside the spec then, no way it should have been installed in this way, but I suspect it was a genuine error in terms of confusion over whether it should have been a 21 or 20 model.

The installer should swap this to dual string at their expense, or replace the inverter with a 21 model - either option would be acceptable IMO, though I'd want the varistors testing to see if they've been damaged.
 
the varistors are like fuses - they either work or don't... so not sure how your going to test them?
They are there to blow in over (more extreme) voltage situations.
Get the installer to split it into 2 strings - don't have them poking around inside the inverter - they are more likely to break it than do anything useful!
(I've only had to change them once in the past 6yrs..and that was a wind inverter with significant over voltage!)
Once in 2 strings you won't have over voltage, so the varistors won't be being 'worked'
 
The varistors aren't fuses as such, they're there to attempt to 'clamp' the input voltage to a safe level. The name comes about because they're 'variable resistors' that have a very high resistance at low voltages and a low resistance at high voltages. They are usually put across the DC inputs and if the input voltage rises too high they start to conduct, disipating some energy and keeping the voltage down. Conducting current and disipating energy degrades them, so if running at high voltages they will eventually fail and then the rest of the inverter input may be exposed to the high voltage (some have a mechanism to test if the varistors are operational).
 
UPDATE!!

I have had a long discussion with sma technical and resolved issue , the overvoltage is due to excellent dc input from mono panels inverter is getting replaced with a higher dc input, no overvoltage will show as panels should not produce more than their 650-700v.
 

Reply to sma overvoltage in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Hello!! I am using 2 ABB 100kw string Inverters (ABB PVS 100-TL) in a single room. Can anyone assist me in calculating the Heat dissipation from...
Replies
1
Views
6K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock