hi all,

doing a consumer unit change in a small shop only has 4 circuits. did a PIR first, all circuits are good.

problem is that I cant find a small consumer unit that is dual rcd. I understand the whole installation can not be protected by one RCD. Is RCBOs the only solution? It boosts the material cost from £60 to £120ish.

any advice would be great.

thanks
 
I agree, RCBOs are the way to go.
I know a lot of the leading brands are abou £30 per RCBO, but there are a lot of cheaper alternatives.
I suppose it depends what wholesaler you use.
I pay £10 per RCBO, I would prefer to use merlin or mk, but would never get any work, and at the end of the day they pass british and EU standards. (it all depends on the customer).
 
I agree, RCBOs are the way to go.
I know a lot of the leading brands are abou £30 per RCBO, but there are a lot of cheaper alternatives.
I suppose it depends what wholesaler you use.
I pay £10 per RCBO, I would prefer to use merlin or mk, but would never get any work, and at the end of the day they pass british and EU standards. (it all depends on the customer).



What make are they,mate,out of interest!!!!!
 
I agree, RCBOs are the way to go.
I know a lot of the leading brands are abou £30 per RCBO, but there are a lot of cheaper alternatives.
I suppose it depends what wholesaler you use.
I pay £10 per RCBO, I would prefer to use merlin or mk, but would never get any work, and at the end of the day they pass british and EU standards. (it all depends on the customer).


I agree wholeheartedly,my friend,but they are not all governed by british fire standards....Again,insurance taking us all up the wrong road....
 

Reply to Small Shop- CU change in the Electricians' Talk | All Countries area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top