Discuss Small voltage from neutral to earth on TT system in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
101
I'm building a house in Azerbaijan, with 3 phase mains supply and TT earthing. The main transformer is at least 800m from my house. Whilst doing my final measurements before going live, I noticed a small voltage between neutral and earth. It varies between 2-4V and seems to be AC. It isn't a stable voltage, it seems that each time I connect the meter probe the voltage is very slightly different, but so far never above 4V.

It dosn't seem like I can do anything about this, my own earth tested OK after I installed it and the earthing of the neutral line at the transformer is what it is - probably not as good as mine.

In case it's relevant, the incoming 3 phase is on aluminium cable, but once it reaches my property everything is 100% copper.

Do I need to worry about this?

Thanks
Philip
 
A small N-E voltage is inevitable in TT or TN-S as there is voltage drop along the neutral cable whenever unbalanced load current is flowing anywhere between you and the substation. Only in TN-C-S will the N & E automatically be at the same voltage at the supply terminals.
 
^^ As above, if all the other test results are fine then a small N-E potential of a couple of volts isn't a problem.
 

Reply to Small voltage from neutral to earth on TT system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
752
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
746
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock