Discuss Smart switch 1 gang 1 way in the DIY Electrical Advice area at ElectriciansForums.net

Tandoori

DIY
Reaction score
0
Hi, i’ve been trying to buy a smart switch 1 gang 1 way but i opened my conventional wall switch and i only have 1 red wire(Live Old UK) 1 black wire(Neutral Old UK) and 1 Green/Yellow(Earth Old UK) but the smart switches have another wire the Load wire, now i’m confused how does this work?
 
TL;DR
Old UK wiring, Smart switch

Attachments

  • IMG_3486.jpeg
    245.6 KB · Views: 8
The black wire is a switched live (L). There is no N at this switch - which is pretty common way of wiring, especially for older houses.
 
The black wire is a switched live (L). There is no N at this switch - which is pretty common way of wiring, especially for older houses.
So would a “No neutral required” smart switch work in replacing the existing switch? Also thank you for explaining this, i had been confused the whole day
 
Yes - buy a smart switch that does not require a neutral.
To work they require a small current to flow through the light fitting all the time. With filament bulbs this is no problem, but with some LED bulbs this can lead to the bulb glowing dimly, or flashing. The workaround is fitting a capacitor/snubber across the bulb, and I believe some no-neutral smart switches provide this component along with their switch.
So it is possible to fit a smart switch, but it's a little more hassle than when you have a neutral (which, as said above, most people in older houses do not have!)
 

Reply to Smart switch 1 gang 1 way in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
362
L
WIRING FOR WALL SMART SWITCH FOR CEILING FAN/LIGHT Just bought a smart wall switch for a ceiling fan/light currently connected to a single switch...
Replies
0
Views
721
littletwinn
L
Hi, I have a 220v House I want to change this switch to smart switch, but I am stumped, I don't have a neutral so I had to return the switch I...
Replies
2
Views
686
I'm trying to replace this standard 2 gand 1 way switch with a smart switch. I've put the both live wires into L in and the switched lives into...
Replies
1
Views
1K
Hi. I am trying to replace a heating timer with a smart switch. The current timer is the type with a dial on the front and 1 to 24 written on it...
Replies
2
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock