Hi All

Just a quick one. Recently had a job to install inter linked smoke detectors in the communal area of a house converted to 2 flats. Health and safety requested standard mains powered smokes with interlink.

I wired this through floors in T+E as I would in a standard domestic property, but have been pulled by another electrician stating it has to be in FP200. I have wired these from the lighting circuit (also wired in T+E) and used radio link bases so wiring it in FP200 seems pointless and pretty harsh reason to fail an EICR?

Any opinions and reg references are appreciated
 
Cables on escape routes should be avoided however not prohibited and should be kept as short as possible if it is necessary. Even if the cable were low smoke the trunking is not and I probably would have used FP. Are you being told why it is not suitable.
 
Might be wrong (Happened before) but don't the rules class a house where 2 or more people live & that are not related as a HMO ?. So although it's been subdivided inside, it may still class as 1 house as with bedsits.
Think I'd be asking the local authority what they class it as.
 
Last edited by a moderator:
From BS5839-6:2013 it sounds like what you have put in is a grade D system, this should however have been communicated to you at tender stage by the specifier. It is implied by the equipment they have told you to install but you should confirm this. If this is the case (Grade D) then BS5839-6:2013 clause 16.5 a) states that "may comprise any cable suitable for domestic mains wiring"
 
Don't think the type of system is relevant it is the wiring method on an escape route. Be interesting to know the comment on the EICR
 
Don't think the type of system is relevant it is the wiring method on an escape route. Be interesting to know the comment on the EICR
If it were a grade A, B or C then he would be using FP. The wiring method described in BS5839-6:2013 states that it should be installed as per BS7671 which doesn't ask for FP on escape routes.
 

Reply to Smoke Detector Wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi all Recently we've been having a few issues with smoke and heat detectors.. been fitting them for years and years now mostly without any...
Replies
14
Views
2K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Good evening all 3 buildings : 1 Gf flat and 1St fl flat year 1915 2nd 6 flats year 1980 3rd cottage year 1900 They are separate buildings...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock