Discuss Socket close to handwash?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

T

TPES

I have first fixed a kitchen area all walls and ceilings plastered.

Now the owner has completely redesigned the layout of the kitchen, so I have a couple of sockets where there of no use now, one of them ends up being behind a very small hand wash bowl, do you think this will be a problem to LABC does it go against any Part P regs?

It's not a full size sink for general use, just a small one to wash hands.. Common sense says there is no serious danger here so could be left, or do you think I'll end up putting a blank plate over this one also??
5e09f4da-7d00-2fb7.jpg
 
It will obviously depend on the individual BCO.
However the general rule of thumb is that a socket-outlet should be 300mm from a sink.
It appears in your case that the socket-outlet is more than 300mm from the sink.
 

Reply to Socket close to handwash?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
833
Hello My dear old mother tried to clean the tiles in our utility room by using a damp rag and I think some water may have dripped into our plug...
Replies
21
Views
4K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
789
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
164
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock