hi, have to wire up one of those whirlpool baths for a client. It comes with a 13amp plug and with reading the new rags I am taking it as that i can put an outlet or fcu under the bath, since its only accessible with a tool. Is this correct???

The whole board will be RCD protected btw. Or shall I run a radial up the other side of the wall to the bathroom, and connect the bath through the wall to an FCu. Help appreciated as always.

Thats regs! sorry!
 
Last edited by a moderator:
Yep, that's fine. As long as all equipotential bonding is in place and the circuit is RCD protected then that is fine.
 
Thanks cirrus, so a fcu under the bath is fine.

I have only main protective equipotential bonding in place. Are you lot still supplementary bonding?? The motor to the whirlpool does however have a fly earth, i would imagine that that should be supplementary bonded?
 
Under the bath is zone zero if a tool is required to access it. If RCD protected supplementary bonding is not required


erm.....no it isnt

if a tool is required to access then its OUTSIDE the zones, regardless of 16th or 17th

Zone zero is IN the bath!!!;)
 
Hmm, how's the head???:)

dont know about 'is 'ed, but mine is banging

i was doing allright, then my nipper came in about 11ish with his mate, woke up this morning, the fridge is empty of 'bow, the spicey rum is gone, the single malt is gone, and that bottle of 80% proof rum from somewhere overseas is looking a lilltle sorry for itself

she was REALLY impressed:eek:
 

Reply to Socket outlets under bath. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
838
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K
Hi guys, I've got a job where I'm installing dado trunking on the floor of an office for sockets and data. Some info on job - In total I will be...
Replies
18
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock