This is scary. You really think it would be OK to remove the RCD because a fault is making it trip? I would love to see your risk assessment for that (that's even assuming it was allowed in domestic).
 
The property should have been rewired as the installation is so dated but the project manager and client didn't want to rewire it. The supply to the flat is approximately 10mm live and neutral tails and earth supplied through the conduit, an approximate length of 20m. Each circuit is wired in singles using steel conduit as the earth.
so you decide to change the board before a EICR done ,so you will cop for the job being done then.
 
In my experience rcd isn’t that tricky to identify the issue once you have unplugged everything and drop all the accessories off. Normally something will become obvious.

I personally would not omit rcd protection because I can’t find the offending item
 

Reply to Sockets tripping after board upgrade - should have been rewired in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
914
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock