Thanks Mike. Alas, the screw heads are about 5cm into the casing via moulded tubes. They are quite small and may be spline headed but v. diff. to see.

Buy a multi bit screwdriver set. Won't cost much for one that will cover most things. Just make sure it is a long reach set though!
 
16A to match what was there. I bought a pack of 5 from amazon. They were too big so I soldered it to the top of the fuse holder as there was plenty of room. I think I paid about £5 for the fuses. Make sure they are fast blow as well otherwise if you use standard blow, if it goes again it'll fry the circuitry.
 
Thanks. Would you mind posting the link to the Amazon fuses in this thread?...it may be too late for me [I think I have fried it now] but others reading will appreciate it. I'll try 'your' fuses as well....I tried a standard 13A fuse at 03:00 this morning after my Much Better Half reported the unit had died....the internal fuse was a right mess..yuk. It popped the fuse immediately. surprise surprise
 
I just looked at my amazon orders. Think I might have got them on ebay as it happens but there are several on amazon at a sensible price. Just search for 16A fast blow fuses. I went for the glass ones cos its easier to see if they've blown. I did hold it carefully over the existing fuse before soldering just to see if it powered up. It did. From memory I just left the old one in place. I have visions in a few years of having a whole ladder of fuses in there
 
I just looked at my amazon orders. Think I might have got them on ebay as it happens but there are several on amazon at a sensible price. Just search for 16A fast blow fuses. I went for the glass ones cos its easier to see if they've blown. I did hold it carefully over the existing fuse before soldering just to see if it powered up. It did. From memory I just left the old one in place. I have visions in a few years of having a whole ladder of fuses in there

Don't use a glass fuse as a replacement for a ceramic fuse, they cannot handle the same level of fault current. It will have been designed with a ceramic fuse for a reason.

Holding a fuse in place over a blown one is an extremely silly thing to do, if the fault which caused the fuse to blow originally was still present you could have sustained serious injury,especially if you are using the wrong size/type of fuse.
 
Thanks. Would you mind posting the link to the Amazon fuses in this thread?...it may be too late for me [I think I have fried it now] but others reading will appreciate it. I'll try 'your' fuses as well....I tried a standard 13A fuse at 03:00 this morning after my Much Better Half reported the unit had died....the internal fuse was a right mess..yuk. It popped the fuse immediately. surprise surprise

If you post a picture of the original fuse someone will probably be able to identify it and advise on where to get it.

Don't try replacing it with the wrong tyoe/size/rating as it may do more harm than good and leave you with much bigger repair bill.
 
I didn't. I replaced a glass fuse with a glass fuse rated identically :) admittedly it was a slightly larger glass fuse but it was rated the same. Admittedly ive done many silly things in my time. To be fair though on this occasion tested all the component's I could first with a multimeter having taken the unit off the wall. I used a phantom power supply to test the led circuit to see if it lit up when I put the fuse in. It did. It wasn't attached to the mains electricity supply. I did fully expect it to blow again when I reattached it to the mains but it didn't. Both it and I survived but I would not advocate anyone else doing it as my level of controlled silliness may not be matched by common sense in others. Thank you for your concern though :)
 
I didn't. I replaced a glass fuse with a glass fuse rated identically :) admittedly it was a slightly larger glass fuse but it was rated the same. Admittedly ive done many silly things in my time. To be fair though on this occasion tested all the component's I could first with a multimeter having taken the unit off the wall. I used a phantom power supply to test the led circuit to see if it lit up when I put the fuse in. It did. It wasn't attached to the mains electricity supply. I did fully expect it to blow again when I reattached it to the mains but it didn't. Both it and I survived but I would not advocate anyone else doing it as my level of controlled silliness may not be matched by common sense in others. Thank you for your concern though :)
Wow…your original fuse was a glass one!

I didn’t see that coming😳
I’ve ordered a pack of fast blow 16A ceramics…. this will be interesting🤔
 

Reply to Solar iBoost died in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

hi there, I have purchased a house with a Solar iBoost. Been working fine for 2 years, went on holiday and switched it off as it had a time...
Replies
10
Views
2K
4
Can someone tell me what the resistance should be for a Solar iboost Clamp? My clamp is regestering zero ohms and I want to confirm this is the...
Replies
0
Views
872
4Dave C
4
Is it possible for all or at least most electricians to be trained up in the wiring of solar PV installations, particularly the iBoost or Eddy or...
Replies
3
Views
1K
Hi all. Bit of a weird one. Have solar PV with a iboost +. All was working fine until meter was exchanged for a smart meter. The system is still...
Replies
3
Views
4K
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock