Discuss Solar iboost not working in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

We have had solar Iboost+ installed in 2018, but it was bought in mid 2016, direct.

It runs 2.5kw oil heater, & has always worked fine. However at 8pm tonight, in walking past it, it was red hot,
the solar panel display said it was off, & it had saved 4.6kwh today, however a bit later it said it had saved 16.4
today, & bit later it had saved NIL, I tested out the connections, with no solar panel power being produced,
On the IBoost, the input was 240v, but circuit A, ** was 520V no load ** B=Nil. Unit said it was OFF.

I have emailed Marlec tonight, this is very concerning, I would have hoped it it went defective, it would be dead,
520v live, when you expected it to be off, & it said it was off, could have been a killer.

We have had solar Iboost+ installed in 2018, but it was bought in mid 2016, direct.

It runs 2.5kw oil heater, & has always worked fine. However at 8pm tonight, in walking past it, it was red hot,
the solar panel display said it was off, & it had saved 4.6kwh today, however a bit later it said it had saved 16.4
today, & bit later it had saved NIL, I tested out the connections, with no solar panel power being produced,
On the IBoost, the input was 240v, but circuit A, ** was 520V no load ** B=Nil. Unit said it was OFF.

I have emailed Marlec tonight, this is very concerning, I would have hoped it it went defective, it would be dead,
520v live, when you expected it to be off, & it said it was off, could have been a killer.


I've also just had this fault. The unit shows 'Water not heating' but the blue lightning symbol flashes. The iboost buddy was showing as importing 3kw so I checked the unit and it was heating immersion heater 1 (showing 480v). I also noticed that even when the panels are producing (say 800w), the unit will show 'heating by solar 2.7kw'. Yet the iboost buddy will show as importing 2kw.
 

Reply to Solar iboost not working in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a 6kw PV with a 6kw Growatt battery and invertor. I have a solar iboost going to the hotwater tank. Recently I had a Ohme Home Pro...
Replies
2
Views
2K
hi there, I have purchased a house with a Solar iBoost. Been working fine for 2 years, went on holiday and switched it off as it had a time...
Replies
10
Views
2K
4
Can someone tell me what the resistance should be for a Solar iboost Clamp? My clamp is regestering zero ohms and I want to confirm this is the...
Replies
0
Views
853
4Dave C
4
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Is it possible for all or at least most electricians to be trained up in the wiring of solar PV installations, particularly the iBoost or Eddy or...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock