Discuss Solar iBoost - Wiring Question in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

R

rugbyref1968

Hi


In the process of installing Solar iBoost
No issues with the unit that needs to be installed in between 16A MCB and Immersion.

Can someone clarify exactly where should install the clamp

I have attached to this post a photograph of the wiring at the Utility Meter.

You will see connections coming from the Utility Meter and the Inverter, each separately going into the block.

Do I attach the clamp on the live cable coming from the Utility Meter to the block or do I attach it to the live cable coming from the block an going to the Consumer Unit

Grateful for comments
 

Attachments

  • 20140814_075029.jpg
    206.6 KB · Views: 103
Make sure you put the clamp on the right way round (you'd be surprised how many don't). If it's dull, you can also do a "kettle test" just to make sure it working by turning the clamp around the wrong way and knocking the kettle on. This makes the iBoost think your exporting and starts to divert energy to the immersion. Just make sure you remember to turn it back again!
 
Wot no seal on the DNO fuse ? who cut that?
Wot not labelled the circuits in the CU?
Wot I can see the inner insulation on the tails going into the henley blocks...
Basic errors - I'd send the apprentice back to fix those...
 

Reply to Solar iBoost - Wiring Question in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

4
Can someone tell me what the resistance should be for a Solar iboost Clamp? My clamp is regestering zero ohms and I want to confirm this is the...
Replies
0
Views
847
4Dave C
4
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
652
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
876

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock