Discuss Solar panel circuit MCB size? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
229
Hi guys,
I have asked this in another Electricians thread here. Firstly what size MCB usually required for lets say a 4kw solar panel load? Also it has been mentioned about RCD's protecting the solar panel circuit may not be a good idea. Any thoughts please? It's a brand new house build.i was planning to install RCBO's to each and every circuit. Thanks http://www.electriciansforums.co.uk...orum/98430-solar-panels-circuit-mcb-size.html
 
See below for info from Samil's product manual. Other inverter manufacturers may have different ideas.


Samil Volt Drop.jpg
 
A 16 A mcb is a reasonable starting point for a system that has a nominal 16 A output.
But it could mean running the mcb near maximum for many hours in the summer.
When in doubt read the manual!
ABB recommend 20 A for the 3.6TL and 25 A for the 4.2TL
SMA recommend up to 32 A for their range from 3000TL to 5000TL
 
There can be a problem with mcbs running hot near maximum rated current. Manufacturers' websites go into more detail. As the cable size for 4 kW PV is generally recommended to be 4 mm2 or larger, there is normally scope for a larger mcb.
 
Last edited:
I will be installing 6mm as I have that on site. No point getting 4mm. Any thoughts about 30mA protection? Am I asking for trouble?

I could always install a 20A MCB if 16A near the limit.
 
"Thanks, according to graph, i could in fact use 2.5mm cable as the inverter is next to the consumer unit. Having said that, installers mentioned 4mm. I've got 6mm, so will use that. I doubt if the circuit will more than 1m."

No, the graph is for the 3300TL model and is given as an example only!! 6mm cable is definitely fine though in a 4kWp domestic situation.
 
A 16 A mcb is a reasonable starting point for a system that has a nominal 16 A output.
But it could mean running the mcb near maximum for many hours in the summer.
When in doubt read the manual!
ABB recommend 20 A for the 3.6TL and 25 A for the 4.2TL
SMA recommend up to 32 A for their range from 3000TL to 5000TL
I don't think we've had a single case of nuisance tripping on any of the 16amp MCB's we've installed on 16A generation limited systems, which would be all of those hundreds of systems.

I've had to swap out a couple of 30mA RCDs for nuisance tripping, but that's it.
 
i think burying DC cables in the wall is an awful idea IMO
How would you normally install DC cables in a new build house? Surly, not surface in say trunking? The Solar people wanted it done that way and agreed the route which is basically straight up from main / inverter area to loft space. They wanted it in steel conduit. I went galvanised, even though it was behind dot dab. I even used female /male brass bushes. Would be interesting to know how you and others would do the job though?
 
i would of tried getting the inverter closer to the array or used micro inverters.
I know nothing about solar installations, just doing to their spec. The distance between the two is not that great really. I would say the depth of a bedroom 3.4m ish plus another 3m. Would you consider that a long DC run? For whatever reason customer or installers wanted the inverter on the ground floor. Possibly for maintenance? Save going up into the loft? I don't know really,I'm just trying to get it done! lol
 
Of course you won't have, a 16A mcb will handle 16A, that's the whole point of it being a 16A rated device.

All well and good as long as G/83 settings applied which limit output. These inverters are made to work in different markets. We had an SMA TL 4.0 that went quite a bit over before it was realised.
 
Because in my view burying them in the wall even in galv conduit, customer turns main switch off in house for whatever reason they still have live cables running down the wall buried! the customer doesn't know they are there, only the person who done the install will.
 
nothing wrong with it but i prefer the inverter up in the loft. Reply With Quote

that way only the ac cable goes to meter then board
reasons not to would include the inverter operating at a higher ambient air temperature when at peak output, and therefore reducing the lifespan of the inverter (which ultimately is dictated by the lifespan of the capacitors), dustier environment, and the inverter being less accessible to check for repairs.

We'll install in lofts when there's no other option, but our preference is for the inverter in a garage or other accessible cooler space within the house if there is the option for those reasons.
 
Because in my view burying them in the wall even in galv conduit, customer turns main switch off in house for whatever reason they still have live cables running down the wall buried! the customer doesn't know they are there, only the person who done the install will.

Then perhaps the customer should read the label at the CU which warns of the dual supply and the location of isolators required to achieve complete isolation
 
reasons not to would include the inverter operating at a higher ambient air temperature when at peak output, and therefore reducing the lifespan of the inverter (which ultimately is dictated by the lifespan of the capacitors), dustier environment, and the inverter being less accessible to check for repairs.

We'll install in lofts when there's no other option, but our preference is for the inverter in a garage or other accessible cooler space within the house if there is the option for those reasons.

agreed but could possibly go in a cuopboard upstairs etc, or just use enphase.
 
All well and good as long as G/83 settings applied which limit output. These inverters are made to work in different markets. We had an SMA TL 4.0 that went quite a bit over before it was realised.

I don't understand, how will the settings cause a 16A mcb to not be able to handle 16A? That is what my post stated, a 16A mcb will be fine with 16A flowing through it.

If what you are saying is that if the inverter could deliver more than 16A if not correctly set up then obviously that is a different scenario.
 
Because in my view burying them in the wall even in galv conduit, customer turns main switch off in house for whatever reason they still have live cables running down the wall buried! the customer doesn't know they are there, only the person who done the install will.
again, if it's mechanically protected what's the problem?

and I mean mechanically protected with proper 3mm thick galv steel.

The stickers on the consumer unit, and fact there's an inverter downstairs and panels on the roof ought to give an indication that there are live dc cables in the wall. We'll always put a DC isolator in the loft as well so it can be isolated if needed.
 
I don't know, I don't install solar. But I do have some common sense and that says you would have a DC isolator where the cables enter the property to isolate them.

yea 9X out of 10 the dc cables will enter the loft so prob would be best to stick a dc isolator there also but the customer aint climbing in to the loft to isolate this are they! they will just crank the ac and dc isolator off at the inverter ( in this case its going to be next to the consumer unit) hence leaving the buried DC cables live in the wall when the main switch at consumer unit,ac isolator/dc isolator at the inverter are all off.
 
isolator in the loft.

Even if there was, which is unlikely if the inverter in elsewhere (very commendable of you though), the customer would just switch of Main AC Isolator for PV (by CU) and assume they had done it. Then they would still get a free crash course in arc welding when they get their drill out.
 
yea 9X out of 10 the dc cables will enter the loft so prob would be best to stick a dc isolator there also but the customer aint climbing in to the loft to isolate this are they! they will just crank the ac and dc isolator off at the inverter ( in this case its going to be next to the consumer unit) hence leaving the buried DC cables live in the wall when the main switch at consumer unit,ac isolator/dc isolator at the inverter are all off.

Then if they can't read a label which clearly states how to isolate correctly what hope has the human race really got?
So what exactly is this scenario you are describing here, why is the customer trying to isolate the installation in the first place?
 
again, if it's mechanically protected what's the problem?

and I mean mechanically protected with proper 3mm thick galv steel.

The stickers on the consumer unit, and fact there's an inverter downstairs and panels on the roof ought to give an indication that there are live dc cables in the wall. We'll always put a DC isolator in the loft as well so it can be isolated if needed.

of course because it will always be an electrician who buys this new build house and knows the ins and outs of an electrical installation/PV system so will automatically assume all this. behave! lol
 
I don't understand what it is you think a house owner is going to be doing to result in them attacking the wall with such force that they can end up breaching the protection of heavy duty galv conduit before realising that they've hit something hard and metallic and should probably stop attacking it and work out what it is.
 
because diy dave has got his big shiny drill out on a sunday!

with the power off, and he just happens to be using a metal drill bit rather than a masonry or wood drill bit?

and is going to just keep drilling despite the drill not going in like it should and sounding like it's hit something metal?
 
because diy dave has got his big shiny drill out on a sunday!

Which is unlikely to operate once he's turned all of the power off. Or if he's using a cordless then I doubt a DIY level cordless drill will be man enough to injure galv pipe.
But either way how many diyers actually switch off their whole house before drilling holes? All that will happen if they do is that it won't go bang when they drill through a cable but probably will when they turn it back on.
 
with the power off, and he just happens to be using a metal drill bit rather than a masonry or wood drill bit?

and is going to just keep drilling despite the drill not going in like it should and sounding like it's hit something metal?

I have to say there are a fair few who do just keep going after they've hit a buried bit of metal, carpenters are quite good at that trick too, along with plumbers and kitchen fitters
 
Thinking about it I've been guilty of the 'get the SDS out and give it some proper welly' approach when encountering resistance whilst drilling a hole. I wouldn't be surprised if most of us are!
 
besides, with the inverter off, even transformerless inverter circuits become protected by dint of being electrically separated.

Switch it back on and the insulation resistance test on start up should detect a damaged cable and not start up, so the circuit stays electrically separated until the fault's repaired.

At the end of the day, it's allowed under BS7671, and it's allowed because it's considered to be safe.
 
besides, with the inverter off, even transformerless inverter circuits become protected by dint of being electrically separated.

Switch it back on and the insulation resistance test on start up should detect a damaged cable and not start up, so the circuit stays electrically separated until the fault's repaired.

At the end of the day, it's allowed under BS7671, and it's allowed because it's considered to be safe.

and that is why i said IMO
 
why would the customer need to go into the loft to isolate it anyway.

if the inverter is in the loft just isolating the ac side will turn the inverter off.

the dc cables will always have potential on them unless the customer covers them on the roof or works at night lol
 

Reply to Solar panel circuit MCB size? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Green2go Launches for All Your Solar, EV Charging and Renewable Needs Green2Go - for All Your Solar, EV Charging and Renewable...
Replies
1
Views
378
Hello, I am a homeowner and have a solar project coming up. I intend to install a 9kw solar system but I am not sure if I have to upgrade my main...
Replies
2
Views
966
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Reaching out for some help/guidance and sanity check. Apologies in advance for the long post, but wanted to make sure it was clear. Thanks in...
Replies
0
Views
988

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock