Discuss Solid Aluminium conductor twin and earth tabulated Zs values? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello,

Board change today (domestic), cable is aluminium twin and earth - socket ring = 4mm/1.5mm, lighting = 1mm/1mm, oven 10mm/4mm

IR all good, continuity & Zs are within values set for copper equivalents.

This is not tinned copper.

I have managed to find out that this cable was used briefly in approx. 1971 due to a copper shortage (flat built in 1971 also). Apparently MK produced accessories specifically for use with this cable, although if ever fitted they are no present now.

Anyway, does anyone here know what the CCP and EFLI for cables sizes mentioned above please?

Obviously departures will be noted on cert.

Thanks.
 
maximum EFLI is related to protective device not the cable type. You may end up with a higher resistance for R1 + R2, but as long as Zs is correct can't see a departure here
 
Not doubting your observations flyingsparc, but you said the lighting was 1mm/1mm cpc could it be that your RFC is wired in the old 7/029 twecc, when Al cable was used lighting was 2.5mm/1.5mm cpc
Just saying thats all
 
If they are within the copper values i cant see a problem.

i can see a massive problem.

the regs prohibit using solid aluminium cables smaller than 16mm for any circuit.
and thats not just the 17th , but 16 , 15 editions also.

so its a big fail now and it was a big fail back in the 60's / 70's when it may have been originally installed.
 
Would it of been a fail to the 14th as I recall 60's / 70's was the 14th edition ? I'll check I've got the old book somewhere from 1972 lol
 
Thanks for replies so far,-

Lighting is solid aluminium 1mm csa, (too small or ali I know) I can be sure its 1mm because I fitted 1mm ferrules (snug) to help terminating in board.

Would be interested to see what 14th said if anything?
 
Thanks for replies so far,-

Lighting is solid aluminium 1mm csa, (too small or ali I know) I can be sure its 1mm because I fitted 1mm ferrules (snug) to help terminating in board.

Would be interested to see what 14th said if anything?

Could be 1/044 that was a solid core lighting cable, the other was probably 3/029 stranded
 
That stuff was called copper clad aluminium, and the lighting cable size was 1.5mm not 1mm and although i may be wrong, but as i recall all cables were stranded!! The copper cladding to these cables, was to make them suitable for existing accessories, so as far as i know, there wasn't any specifically made accessories... This stuff only lasted a very short time it wasn't very successful.


I know of at least 2 large private housing estates that were all wired in that copper clad cable. I did hear many of them were rewired by the owners a few years down the line!! ...Horrible stuff!!
 
That stuff was called copper clad aluminium, and the lighting cable size was 1.5mm not 1mm and although i may be wrong, but as i recall all cables were stranded!! The copper cladding to these cables, was to make them suitable for existing accessories, so as far as i know, there wasn't any specifically made accessories... This stuff only lasted a very short time it wasn't very successful.


I know of at least 2 large private housing estates that were all wired in that copper clad cable. I did hear many of them were rewired by the owners a few years down the line!! ...Horrible stuff!!
Aye there's a lot of CCA data and telecoms cable kicking about lately,and its horrible,Had to pull in 100mtrs cat 5 at the farm,connected up tested and faulty,a break in a core somewhere,only when I looked at the box later did I realise it was CCA,otherwise I would have sent it back straight away,seems as brittle as hell.
 
Thanks again for the responses.

I don't have a copy of 14th edition, (I was only 3 years old in 1971).

If any one still has a copy, would you mind having a look in it for me, for current carrying capacity please?

Or any publshed data?

Many thanks.
 
14th Ed has aluminium PVC covered from 16mm only. It lists copper clad aluminium from 1.5 (1/1.38) clipped direct 12A. 2.5 (1/1.78) 17A. 4mm ((7/0.85) 22A.

I have a customer with aluminium cable throughout the house. It is aluminium; I cannot see any copper coating on it. It is slightly larger than the normal metric cable so I am assuming it has similar rating to the equivalent copper cable. All the accessories I touch are loose. Look up aluminium cable on Google, there is a lot of it in America and they have done a lot of work on the problems and methods of rectification.
 

Reply to Solid Aluminium conductor twin and earth tabulated Zs values? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I visited a client about a week ago, an elderly couple complaining that their lounge, hall and landing lights were all flickering simultaneously...
Replies
49
Views
6K
I do seem to pick only the weirdest properties to inspect... Victorian terraced house today - with up front RCD to a Wylex fuse board and main...
Replies
24
Views
3K
We recently had a thread or two about some cables that were almost certainly tinned copper, but people continued to suspect they were aluminium...
Replies
7
Views
2K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock