Discuss Some advice needed! Testing in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi,

I’m wondering if anyone would know that when I switch a light switch off I am still getting 40v at the light. I have ir tested all of the circuits in the installation and all passes. Surely this means they’re is a leakage though? 40v is a bit too high?
 
Hi,

I’m wondering if anyone would know that when I switch a light switch off I am still getting 40v at the light. I have ir tested all of the circuits in the installation and all passes. Surely this means they’re is a leakage though? 40v is a bit too high?
What were the IR test results?
 
Can you be a bit more specific about 'having 40V at the light'. Measured between which two points? What did you get for these:
L-E voltage?
N-E voltage?
L-N voltage?
And as Pete says - what were ther IR figures?
 
False reading caused by pick-up sounds likely.
You need to be specific and accurate with your measurements though. Voltages are between two points, not 'at somewhere'. IR readings are in MR, not mR - unless the reading you gave us was indeed in milliohms. And between which 2 points was the IR reading you gave taken?
 
False reading caused by pick-up sounds likely.
You need to be specific and accurate with your measurements though. Voltages are between two points, not 'at somewhere'. IR readings are in MR, not mR - unless the reading you gave us was indeed in milliohms. And between which 2 points was the IR reading you gave taken?

The reading is between L- E.
 
False reading caused by pick-up sounds likely.
You need to be specific and accurate with your measurements though. Voltages are between two points, not 'at somewhere'. IR readings are in MR, not mR - unless the reading you gave us was indeed in milliohms. And between which 2 points was the IR reading you gave taken?
Good point on the use of capitals DPG never gave that a thought.
 
Is it actually causing a problem or is it just something you've noticed?
Since it's below 50v I'd put it down to being induced from elsewhere (seems more common with singles) and move on.
 

Reply to Some advice needed! Testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
1K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
614
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
I’m just finishing my L2 2365 at college in the evenings and plan to do the L3 2365 with the same college as an evening course. However I would...
Replies
0
Views
266
Hi everyone, I recently moved out of my rented property, and as expected, my landlord is attempting to withhold a significant portion of my...
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock