Discuss Some basement basement lights not turning on, or delayed on. in the DIY Electrical Advice area at ElectriciansForums.net

tommymc

DIY
Reaction score
2
Hi, I'm a new DIY member hoping to get some suggestions on a (to me) perplexing problem with my basement overhead lights. There were originally 4 of them, and through the years, I've added 4 more by running cable from the existing fixtures. They are all controlled by three 3-way switches which turn all the lights on at once. I've also run several outlets on the same circuit for the workshop. I've had the same basic setup for 30 yrs. Two days ago, an issue developed where one light came on as usual, then there was a long delay before others started cascading on. By yesterday, this delay had reached several minutes. Last night, it deteriorated further, and only 3 lights come on, no matter how long the wait. All the lights are LED bulbs screwed into ceramic fixtures. I also don't think they are coming up to full brightness. I've tried replacing bulbs, and have an incandescent that works in some fixtures but not others. I've unplugged all my power tools so there's nothing on the circuit other than the overhead lights.

I'm not sure how to troubleshoot this. An open connection or mouse-eaten wire wouldn't seem to explain the delayed on. An explanation for what could delay or dim bulbs that test perfectly well in other fixtures would give me a starting point. This all came on suddenly, with no apparent trigger event. Any suggestions will be greatly appreciated.

Edit/update: According to my understanding of the original circuit, there were 4 ceramic fixtures which I'll order 1,2,3 & 4 in the order I believe they're wired. #1 always comes on, and for testing that's where the incandescent bulb is. #2 (LED) comes on, although it seems dim. When I put a bulb (LED) in #3, it comes on for a second, then goes out and #2 comes on. wtf? #4 doesn't come on at all. I've also disconnected the feed to the workshop lights and receptacles, which all came through #2.
 
Last edited:
SOLVED! Suspecting low voltage might be causing the strange LED behavior, I put a multimeter on the #2 fixture and measured only 50 volts. Next I opened the only other original fixture (#4) that had newer lights tapped into the box.....and found a burnt mess. The original wires (which had been crimped and taped) were fried.....insulation melted and broken copper. The smoking gun, so to speak. I don't know why the breaker didn't trip, or how any voltage was still going through the circuit. I also don't know what caused the melting in a box that hadn't been touched for close to 30 yrs. After trimming back the wires and replacing the fixture, all seems back to normal. Thanks to anybody who reads this and has any comments.
 

Reply to Some basement basement lights not turning on, or delayed on. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
488
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
596
My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
Replies
10
Views
909
I am adding a light fixture in a room I am restoring in my 160 yo house. I have ran a new 12-2 w/ground wire from the ceiling box to a junction...
Replies
2
Views
881
Hi all, No change to electric wiring and supply and no change to the previously working light bulbs but now when I turn the 2 wall lights in my...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock