Octopus

Today I got a call from a lady today, asking me if I could come and provide a price to move a socket.

So I duely turned up at the prearranged time.....

1. The had ordered a new cooker from Comet - who had turned up to install it and have refused due to the location of the socket above being "illegal"

Cooker.jpg

2. They've marked the two tiles where a new socket would be OK as the new cooker is a gas unit and only requires a socket (13a plug) supply

3. No RCD protection in the house - so a single RCD socket in the kitchen would be required!

4. No bonding to the gas and water - and the CU is on the opposite side of the detached house - clearly didn't like hearing about the requirement to add this before I can do anything.


This couple are elderly, and judging by the home and their reaction to what I said, don't have much money.

So what would you do.....

1. Play by the rules, insist on the bonding, RCD socket, etc??

or

2. Bend the rules and forget the bonding and RCD's??

Oh happy days!
 
Last edited by a moderator:
the ideal remedy would to blank off the offending socket, extend the cables to a new socket below worktops, do the earthing and bonding, and fit RCD to the relevant circuit. obviously, cost is going to be a factor. if the clients are elderly, then there may be grant assistance from the local council.
 
What about changing the double socket for an rcd fcu and mt to socket behind cooker.
Not ideal but takes the plug and socket out of the frame. The bonding is another matter, but at least the new wiring is protected.
 
Surely we want the system to be as safe as possible for an elderly couple, not bend the rules because we "assume" they have no money.
Treat all customers the same as far as regs go imo. If you want to give them a special rate for your labour then obviously that's your call.
The socket needs moving.
 
Makes you wonder why the ignition system needs a mains connection, it ain't that hard to generate a spark from a battery source! Lazy manufactuers.

If they're an elderly couple I'd do the bonding for material cost only....coz I'll be there in a few more years :)
 
I agree - option 2
BUT you know fine well, this is the job where something goes wrong ie chip pan fire, fire brigade investigate, the old couple sing like canaries cos their insurance won't pay up, mention about you and the socket. Next thing your standing in front of guy in wig, waving a big green book in front of you saying "you know better blah blah"
i would stick to your gut feeling and do the job properly, you have NOTHING to gain by taking option 1
 
so youre not going to help them out ?
what a nice man :-/

Tbh, I don't help anyone out if it involves breaking the regs. I often help people out by supplying materials at cost or reducing my rate, but not if it involves compromising my standards.
I know this has been said before, but never assume that just because they are old, they are poor. I have come across many elderly living in rags with their heating down low, then I speak to their children who moan about the cash they have stashed and won't spend.
 
Tbh, I don't help anyone out if it involves breaking the regs. I often help people out by supplying materials at cost or reducing my rate, but not if it involves compromising my standards.
I know this has been said before, but never assume that just because they are old, they are poor. I have come across many elderly living in rags with their heating down low, then I speak to their children who moan about the cash they have stashed and won't spend.

that post is worthy of a facepalm of epic proportions.
i hope that you can still afford such high principles on a state pension.
 
Tbh, I don't help anyone out if it involves breaking the regs. I often help people out by supplying materials at cost or reducing my rate, but not if it involves compromising my standards.
I know this has been said before, but never assume that just because they are old, they are poor. I have come across many elderly living in rags with their heating down low, then I speak to their children who moan about the cash they have stashed and won't spend.

And don't presume that just because they are old they are not poor. In some cases, I would agree. However, in todays society, if choosing between moaning 'children', who think they are owed something for nothing, and oap parents, I know who I'd believe in most cases. Best case scenario, do things correctly but try not to leave them in the ****, unless they deserve it.
 
Makes you wonder why the ignition system needs a mains connection, it ain't that hard to generate a spark from a battery source! Lazy manufactuers.

If they're an elderly couple I'd do the bonding for material cost only....coz I'll be there in a few more years :)
that cooker has an electric oven/gas hob
 
Min hieght to any combustable item or otherwise above as Gas hob is 750mm , 650mm Elec , I think they where more concerned over the lead , ie glass getting hot / melting lead . Nothing stopin them using an extention lead if they want to from another source . Ps if its not fitted and gased in , Whats the pan for ?? pmsl , Just blank it of for them ,,,,,,,, Also what are comet doin providing a new appliance with no piggin plug ?????????????
 
Last edited:
I'd put in writing any extra work (like the bonding) quoteing the regs and potential dangers if the extra work wasn't carried out adding a quote for the extra work to be done.That way (in my mind) the customer then has the option to have upgrades done at a later stage or straight away.

I realise by the regs we have to do this, that and the other but i still personaly think it's morally wrong to literally force people to spend far more than they'd ever expect to 'move a socket so they can cook a meal'.

Do the job that's been asked for (in this case move the socket) and quote for earthing to meet the reg's in writing...to me this is how it should be......I didn't become a sparks to force more cash out of people's pockets by using the regs to force them into having more work done....it's thier money and thier option how to spend it.

Obviously is something is an immediate danger they either pay for it to be repaired correctly or i leave it disconnected.
 

Reply to Some times I really feel sorry for some clients in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top