Discuss Sort circuit capacity bs1362 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

ok liam good luck tomorrow. page 50 , 1362 fuse. let me know how you get on.

regarding the bs3036

The BS1362 your most likley to find in the PAT testing book (purple coloured if i remember back)

Jamie if you ment breaking capacity instead of scc look at the following:

BS 1362 specifies breaking-time/current characteristics only for fuses with a current rating of 3 A (marked in red) or 13 A (marked in brown). Examples for the required breaking-time ranges are

  • For 3 A fuses: 0.02–80 s at 9 A, < 0.1 s at 20 A and < 0.03 s at 30 A.
  • For 13 A fuses: 1–400 s at 30 A, 0.1–20 s at 50 A and 0.01–0.2 s at 100 A.
 
Last edited:

Reply to Sort circuit capacity bs1362 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
155
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
596

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock