Discuss Spilt tea need help fast! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi spilt tea on a single socket outlet with a plug in it. The fuse on the plug went off. Changed the fuse with the same amp rating. Tried it in one of the sockets in the room none of them are working. I dried the socket out abit with a towell but im assumig the liquids went further. What to do none of the sockets are working in the room whereas other room ones are working. Circuit breaker hasnt tripped. Waited 8 hrs for socket to dry to see if it works no luck.
 
Can you go to your Consumer Unit and look for any switches in the off position (that's usually down). Try putting to on (usually up) . If it immediately clicks off, don't try it again.
And report :)
Do what Wilko suggests, if the trip trips immediately, you will need the expertise of an Electrician to test the circuit involved. Probably judt residual dampness, but to be safe get a Spark in to take a look, if he is any good it shouldn't cost you very much, but what cost family safety? Don't mess withe the electrics yourself, it's not worth the risk. Where are you situated, could be a Forum Member is near to you and would be willing to help.
 
Can you go to your Consumer Unit and look for any switches in the off position (that's usually down). Try putting to on (usually up) . If it immediately clicks off, don't try it again.
And report :)
All ccu switches were up when the tea spilt and fuse blew. I turned them off and on and they dont trip at all. Checked wiring looked fine no damage to sheathe or copper. Im thinking the outlet needs replacing?
 
Sorry, SWD... I had to disagree.... We don't know how capable the OP is with electrics and asking him to remove a socket may be too far from his ability.
Best advice is to get an electrician in.
 
Disconnect wet socket make cables safe then try powering up the circuit.

How many sugars in the tea BTW?

2 :)

I disconnected the socket and checked wires brushed off some dust hehe and reconnected them still no power. Theres an electrician working 2 doors away from me so might get him to have a look but wanted to see if i can solve it myself without burning the house down as ive got my lvl 3 electrics qualification :) ill be sure not to and take full precaution
 
Disconnect wet socket make cables safe then try powering up the circuit.

How many sugars in the tea BTW?

2 :)

I disconnected the socket and checked wires brushed off some dust hehe and reconnected them still no power. Theres an electrician working 2 doors away from me so might get him to have a look but wanted to see if i can solve it myself without burning the house down as ive got my lvl 3 electrics qualification :) ill be sure not to and take full precaution. But yh any other suggestions would help
 

Reply to Spilt tea need help fast! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
728
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi New to this forum, Just looking for some advise as a DIY person. I have recently purchased a new home. I have come across a wall light which...
Replies
11
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock