Ahhh, I see, I was trained under the 17th. So presumably he has either been misinformed or has got the wrong end of the stick. I have always assumed it would be treated similarly to T+E, but from what you say it could have been used in the same way as a SWA pre 17th ed?
 
Why are you limiting your available supply to 63A ?

Your SF needs to be within 3m of the incomer/meter, this is to satisfy the DNO by not relying on their service fuse, you can use an 80A SF to fulfil this requirement, a 63A SF won't discriminate with the DNOs 80A fuse anyway.

I have to admit I wasn't aware of this, I may as well use an 80A fuse. I had assumed that discrimination would still be an issue. Thanks!
 
The Rule of Thumb is "An upstream fuse will discriminate with downstream fuse of half it's rating."

True, but we are not trying to discriminate here, it is only to satisfy the DNO, they don't like you relying on their service fuse past about 3m, I believe it is also so they can guarantee their Ze figure, they have to draw the line somewhere as to what they will accept, the 3m rule seems to be about being reasonably practical in this regard, after your SF is your problem so to speak ;) .
 
True, but we are not trying to discriminate here, it is only to satisfy the DNO, they don't like you relying on their service fuse past about 3m, I believe it is also so they can guarantee their Ze figure, they have to draw the line somewhere as to what they will accept, the 3m rule seems to be about being reasonably practical in this regard, after your SF is your problem so to speak ;) .

Totally agree, I was just pointing it out lol
 
Hmm. This isn't something I was ever taught. So if I have a 40A Submain DB, does this mean that I can only have 20A circuits fed from it?

No, it means that a fuse greater than 20A will not discriminate with the submain fuse, so you would need to select an alternative OCPD for the final circuit which does discriminate.
 

Reply to Split Concentric as a submain in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Replies
9
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
467
Evening all, I found my first ever split concentric cable today. Running from an isolator up and into a flat. I was doing an EICR. I could not...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top