how doi enlarge the pic big enough to read it? i can just read "circuit details" , but none of the entries.
You often find that Zs is higher than R1 + R2. Remember Zs = Ze + R1 + R2.thats what i thought as well, look at the second socket circuit the Zs reading is higher than the R1 + R2 reading
You often find that Zs is higher than R1 + R2. Remember Zs = Ze + R1 + R2.
That happens quite a lot as well, parallel earth paths. Especially with metal conduit.sorry spin i posted that wrong lol the R1 + R2 is higher than the Zs reading
Left click on the image, then you should get a magnifying glass with a + in it.
Remember to back page, rather than close the window, otherwise you'll close the browser.
That happens quite a lot as well, parallel earth paths. especially with metal conduit.
I have seen this quite a lot. They used to say that you were not allowed to do a ZS reading at any point other than a socket due to the exposure of live parts (with a socket you can use a plug top tester) so the only way to get a Zs was (R1+R2)+Ze, the R1+R2 that is lower than the Zs is most likely due to a parallel earth path (eg bonding) and as this was the only real test, shows in the results. Not sure what the norm is in regards to Zs testing now, I just throw the covers off and get in their with my tester.
by calculation, you are correct, but due to parallel paths (water pipes etc.) to earth, the Zs can be lower than calculated. this is most noticeable in TT systems where the resistance to earth through services is less than the resistance through the earth rod.
by calculation, you are correct, but due to parallel paths (water pipes etc.) to earth, the Zs can be lower than calculated. this is most noticeable in TT systems where the resistance to earth through services is less than the resistance through the earth rod.