Hi guys, I wonder if someone would be kind enough to help me understand the answer to this question from a well known guide-book on 'Inspection, testing and certification of Electrical Installations', 'cos I can't work it out for the life of me!
Q: A ring circuit is wired in 4mm[SUP]2[/SUP] singles in conduit. The circuit is 87 metres in length and is protected by a 32A BS 3871 type 2 circuit breaker, the maximum Z[SUB]s [/SUB]permissible is 1.07 ohms and the actual Z[SUB]e [/SUB]is 0.63 ohms.
Calculate:
(i) The expected Z[SUB]s
[/SUB](ii) The maximum permissible length that could be allowed for a spur in 4mm[SUP]2 [/SUP]cable.
A: (i) From Table 9A in the On-site-Guide 4mm[SUP]2 [/SUP]copper conductors have a resistance of 4.61 m-ohms/M.
R[SUB]1[/SUB]+R[SUB]2 [/SUB]for the phase and CPC both in 4mm[SUP]2[/SUP] is 9.22 m-ohms/M
R[SUB]1[/SUB]+R[SUB]2[/SUB]:
9.22 x 67 = 0.061 ohms
1000
As it is a ring:
0.61 = 0.15
4
The R[SUB]1[/SUB]+R[SUB]2[/SUB] value is 0.15 ohms.
Z[SUB]s [/SUB]= Z[SUB]e[/SUB] + R[SUB]1[/SUB]+R[SUB]2
[/SUB]0.63 + 0.15 = 0.78 ohms. As the maximum permissible given as 0.86 ohms this value is acceptable.
(ii) As the maximum permissible Z[SUB]s[/SUB] is given as 0.9 and is taken from the On-Site-Guide, no correction for temperature is required. We must subtract the Z[SUB]e[/SUB] from the actual Z[SUB]s[/SUB] to find the maximum permissible R[SUB]1[/SUB]+R[SUB]2[/SUB] value.
R[SUB]1[/SUB]+R[SUB]2 [/SUB]= 0.9-0.63 = 0.27 ohms
We must now subtract the actual R[SUB]1[/SUB]+R[SUB]2[/SUB] value from the maximum permissible value.
0.27-0.15 = 0.12
The maximum resistance that our spur could have is 0.12 ohms. To calculate the length we must transpose the calculation:
mV x length = R
1000
to find the total length transpose to
R x 1000 = length
mV
Therefore:
length =
0.12 x 1000 = 13 metres
9.22
Total length of cable for the spur will be 8.67 metres.
Now, this is typed out pretty much exactly as per the book, and the first thing is that although the question is talking about an 87M run, the answer is based on 67M. So i figure presumeably a typo, and go with the value of 67metres for the purposes of the calculations, and I follow all the thinking (even allowing for the fact that the quoted maximum Z[SUB]s[/SUB] for a 32A 3871 type 2 CB in the current OSG is 0.83 ohms, not 0.90), right up 'till point number (ii). The answer states that the maximum Z[SUB]s[/SUB] is given as 0.9?!! (A rounded-up 0.86?), and I understand that you would take away the Z[SUB]e[/SUB] to get your max R[SUB]1[/SUB]+R[SUB]2[/SUB], and then subtract the previously worked out R[SUB]1[/SUB]+R[SUB]2[/SUB] value, to find out what R[SUB]1[/SUB]+R[SUB]2[/SUB] you've got left to 'play with', but how is the final figure of 8.67 metres arrived at? I can't see what I'm missing, and it's driving me mental!! :crazy: Cheers to all in advance for any insight into this!
Q: A ring circuit is wired in 4mm[SUP]2[/SUP] singles in conduit. The circuit is 87 metres in length and is protected by a 32A BS 3871 type 2 circuit breaker, the maximum Z[SUB]s [/SUB]permissible is 1.07 ohms and the actual Z[SUB]e [/SUB]is 0.63 ohms.
Calculate:
(i) The expected Z[SUB]s
[/SUB](ii) The maximum permissible length that could be allowed for a spur in 4mm[SUP]2 [/SUP]cable.
A: (i) From Table 9A in the On-site-Guide 4mm[SUP]2 [/SUP]copper conductors have a resistance of 4.61 m-ohms/M.
R[SUB]1[/SUB]+R[SUB]2 [/SUB]for the phase and CPC both in 4mm[SUP]2[/SUP] is 9.22 m-ohms/M
R[SUB]1[/SUB]+R[SUB]2[/SUB]:
9.22 x 67 = 0.061 ohms
1000
As it is a ring:
0.61 = 0.15
4
The R[SUB]1[/SUB]+R[SUB]2[/SUB] value is 0.15 ohms.
Z[SUB]s [/SUB]= Z[SUB]e[/SUB] + R[SUB]1[/SUB]+R[SUB]2
[/SUB]0.63 + 0.15 = 0.78 ohms. As the maximum permissible given as 0.86 ohms this value is acceptable.
(ii) As the maximum permissible Z[SUB]s[/SUB] is given as 0.9 and is taken from the On-Site-Guide, no correction for temperature is required. We must subtract the Z[SUB]e[/SUB] from the actual Z[SUB]s[/SUB] to find the maximum permissible R[SUB]1[/SUB]+R[SUB]2[/SUB] value.
R[SUB]1[/SUB]+R[SUB]2 [/SUB]= 0.9-0.63 = 0.27 ohms
We must now subtract the actual R[SUB]1[/SUB]+R[SUB]2[/SUB] value from the maximum permissible value.
0.27-0.15 = 0.12
The maximum resistance that our spur could have is 0.12 ohms. To calculate the length we must transpose the calculation:
mV x length = R
1000
to find the total length transpose to
R x 1000 = length
mV
Therefore:
length =
0.12 x 1000 = 13 metres
9.22
Total length of cable for the spur will be 8.67 metres.
Now, this is typed out pretty much exactly as per the book, and the first thing is that although the question is talking about an 87M run, the answer is based on 67M. So i figure presumeably a typo, and go with the value of 67metres for the purposes of the calculations, and I follow all the thinking (even allowing for the fact that the quoted maximum Z[SUB]s[/SUB] for a 32A 3871 type 2 CB in the current OSG is 0.83 ohms, not 0.90), right up 'till point number (ii). The answer states that the maximum Z[SUB]s[/SUB] is given as 0.9?!! (A rounded-up 0.86?), and I understand that you would take away the Z[SUB]e[/SUB] to get your max R[SUB]1[/SUB]+R[SUB]2[/SUB], and then subtract the previously worked out R[SUB]1[/SUB]+R[SUB]2[/SUB] value, to find out what R[SUB]1[/SUB]+R[SUB]2[/SUB] you've got left to 'play with', but how is the final figure of 8.67 metres arrived at? I can't see what I'm missing, and it's driving me mental!! :crazy: Cheers to all in advance for any insight into this!