I'm trying to install a 3 pin socket, high above a door, for an Echo Dot the idea is so it doesn't 1. Get in the way; 2. Take up a an existing socket.

I've got a pull string light switch right next to where I want to install it and, because the draw isn't going to be too much from the light circuit, I want to take a feed from this switch, to the socket.

I've got as far as wiring it all in, but unfortunately, the power to the socket is only there when the light is OFF. If I switch it on, the power to the socket dies. Back on again, and the Echo switches off.

Is there anything I can do to allow constant power to the socket, and allow the light switch to work as it should??

Thanks in advanced!
Bobby.
 
You don't say what cable(s) are in the light switch, but very likely there is one switch drop cable, which has a L and switched L (plus earth). The switched L if black or blue, should be sleeved with red or brown to indicate L (but often it isn't).

It sounds like with the switch off, you are powering the socket through the light, and because the item plugged in takes so little current, the light appears to stay off (though actually will be slightly powered).

You need to disconnect the socket from this switch, and have it powered from a socket circuit in a way that meets current regulations (which includes RCD protection for any new sockets).
 
Important note: I'm not an electrician.

But - you say there is a pull string here - why - where is it? I ask because the regs are pretty clear in covering electrical works around bathrooms etc., and for good reason mate.

I think you should share any pics you have, of the wiring so far and the set-up.
 

Reply to Spur socket from light switch in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
412
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
701
I have a single wall switch powering 1 light and I want to add a separate light and change to wall switch to a double to power them both...
Replies
4
Views
383
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock