Discuss Spurring off a ring in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
Hi,

I only have 1 socket in one my rooms but would like to install 2 more double sockets, the kitchen backs onto the room and i thinking about spurring of the one of the sockets in the kitchen, i was going to install fused spur (fused 13A) then off the load side install 2 double sockets. Is this ok? meet current regs?

All help appreciated

Thanks
 
Last edited:
Could i extend one of the cables using 30amp connector blocks in the back box of the existing socket, then i could make the 2 new sockets part of the ring?

any thoughts on this?
 
Could i extend one of the cables using 30amp connector blocks in the back box of the existing socket, then i could make the 2 new sockets part of the ring?

any thoughts on this?

Nothing to say you couldn't, not ideal though, if connections are done correctly I would use wagos instead of connector block, and change the back box to a 47mm give some room
 
just a thought, does it have a separate kitchen ring? don't like the idea of 2 sockets in one room fed off the kitchen ring and the other fed off the house ring, I know its not against regs but always the potential for some numpty to attempt diy in the future.
 
just a thought, does it have a separate kitchen ring? don't like the idea of 2 sockets in one room fed off the kitchen ring and the other fed off the house ring, I know its not against regs but always the potential for some numpty to attempt diy in the future.

Nothing usual about this at all. Very common imho
 
just a thought, does it have a separate kitchen ring? don't like the idea of 2 sockets in one room fed off the kitchen ring and the other fed off the house ring, I know its not against regs but always the potential for some numpty to attempt diy in the future.
It sometimes can't be avoided, and to be fair anybody working on the circuit(s) in future should know what they are doing anyway, true?
 
It sometimes can't be avoided, and to be fair anybody working on the circuit(s) in future should know what they are doing anyway, true?
no doubt about it all! but should know what they are doing and actually knowing what they are doing are 2 different things, like ive said its not against regs and yes it will happen in lots of places just not something I like to do.
 

Reply to Spurring off a ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
699
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
216
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
If someone made a request to you, to install a new double socket that would be supplying power to a tumble dryer along a circuit that does not go...
Replies
12
Views
463
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
408

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock