Discuss Staircase timer with pir sensors in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I have replaced a staircase timer because the previous one was fault. There was a problem the light stayed on all the time. When i replaced the new one and awitched on the mcb light when on for some time then switched off. When i oass in front of pir sensor they dont switch on. The sensir is clicking. Can thebproblem be a sensor?
 
Welcome to the forum mate.
What testing have you done on the circuit?
 
The sensors go wrong all the time, many were originally wired with inductive loads. (this may not apply in your case).
In my experience the most common mode of failure is staying on, this can be time intensive if many are wired in parallel.
Remove the trigger from the staircase timer and terminate it safely and see if it remains live after the pir timer has passed.
 

Reply to Staircase timer with pir sensors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I replaced a Flash immersion timer with an apt one today and it seemed straightforward but just wondering should the light on isolation switch...
Replies
5
Views
392
Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...
Replies
4
Views
410
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
532
Hi there, I have an outside light that is turned on with a switch from inside and would like to change it to a PIR version incorporating an...
Replies
8
Views
1K
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
793

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock