Hi Guys,

Is my understanding of why it is bad for a star/delta motor to be stuck in star correct?

1) Star delta starting is used as a method of starting larger motors at a reduced voltage of root 3 , which reduces the large starting current drawn by the motor during start up, therefore protecting the stator windings from burnout due to overheating. As the voltage across the motor windings are reduced by root 3 during starting in Star, this causes the line current drawn to be reduced to one third of the delta current.

As the torque will be reduced according to the square of the applied voltage; if the voltage is reduced by a factor of root 3, then the starting torque in star will be reduced by the square of the factor,therefore by a factor of 3, which reduces the starting torque to one third of the delta torque.

The power output of the rotor is also reduced to one third of a delta connected motor.

The design requirements of the motor is allow it to be started in star BUT run in delta, to match the required torque and power requirement of the driven load.

Therefore by running the motor in star means running the motor at one third of the torque and power output, meaning that the rotor will not match the required torque and power demand by the load, therefore the motor will stall and overheat.

Can you please pick out any technical inaccuracies in my answer.



Thanks,

Ewan
 
One of the main reasons for star delta starters is to reduce the starting current that would occur if the motor was switched direct to delta. DNO's often put limits on starting currents.
 
Hi Guys,

Is my understanding of why it is bad for a star/delta motor to be stuck in star correct?

1) Star delta starting is used as a method of starting larger motors at a reduced voltage of root 3 , which reduces the large starting current drawn by the motor during start up, therefore protecting the stator windings from burnout due to overheating. As the voltage across the motor windings are reduced by root 3 during starting in Star, this causes the line current drawn to be reduced to one third of the delta current.

As the torque will be reduced according to the square of the applied voltage; if the voltage is reduced by a factor of root 3, then the starting torque in star will be reduced by the square of the factor,therefore by a factor of 3, which reduces the starting torque to one third of the delta torque.

The power output of the rotor is also reduced to one third of a delta connected motor.

The design requirements of the motor is allow it to be started in star BUT run in delta, to match the required torque and power requirement of the driven load.

Therefore by running the motor in star means running the motor at one third of the torque and power output, meaning that the rotor will not match the required torque and power demand by the load, therefore the motor will stall and overheat.

Can you please pick out any technical inaccuracies in my answer.
No such animal as a Star Delta Motor, star delta is a method of starting a 3 phase Motor , sorry meant for the OP
Thanks,

Ewan
 
My two cents:
Star delta starting is used as a method of starting larger motors at a reduced voltage of root 3 , which reduces the large starting current drawn by the motor during start up, therefore protecting the stator windings from burnout due to overheating. As the voltage across the motor windings are reduced by root 3 during starting in Star, this causes the line current drawn to be reduced to one third of the delta current.
Generally agreed, section crossed out is not a given. As stated above it reduces startup/inrush currents. It isn't a given the windings would overheat. It may cause problems with protective devices operating though.
As the torque will be reduced according to the square of the applied voltage; if the voltage is reduced by a factor of root 3, then the starting torque in star will be reduced by the square of the factor,therefore by a factor of 3, which reduces the starting torque to one third of the delta torque.
Agreed, the lower torque is the price paid for the lower current.
Therefore by running the motor in star means running the motor at one third of the torque and power output, meaning that the rotor will not match the required torque and power demand by the load, therefore the motor will stall and overheat.
That very much depends what the motor is doing and I don't think you can generalise to this degree. You can certainly say you have reduced torque while running in star configuration.
I think you have the right idea about how it is working, but are being a little dramatic about the consequences!
 
If the motor has a load applied to it and has been designed to run in delta with this load then running in star with a reduced torque for a period of time may not be a wise thing. If the motor is cooled by veins and fan then this effect is also reduced.
 
@timhoward gives some good explanations there and I don't have much to add. I have seen 400/230V motors running permanently in star due to mis-connection, where the problem was not immediately noticed because the load did not demand full torque or exact speed from the motor at any time. One example was an organ blower with a 5hp 4-pole motor that was suspected of delivering slightly low pressure. It was wired in star and slipping too much, achieving something like 1350 rpm instead of 1425, and it wasn't quite keeping up . The motor itself was completely unharmed.

I would amplify that burnout of the windings with DOL starting is most unlikely. Even large motors can often be started DOL but with unpleasantly high starting currents. A squirrel-cage motor can easily take 5x FLC at standstill, so the above blower example would take upwards of 40A, which would cause the lights sharing the submain to dip visibly (you can just about see the dip with star-delta starting).

The actual starting torques and currents at different voltages depend somewhat on the design and size of the motor, not just on the theoretical ratios. At a standstill the slip frequency is equal to the supply frequency and the rotor cage inductance plays a major part in determining the torque, since the current is seriously out of phase with the stator flux wave. Hence the advantage of rotor-resistance starting over star delta, as this improves the rotor pf as well as limiting the current.
 
@timhoward gives some good explanations there and I don't have much to add. I have seen 400/230V motors running permanently in star due to mis-connection, where the problem was not immediately noticed because the load did not demand full torque or exact speed from the motor at any time. One example was an organ blower with a 5hp 4-pole motor that was suspected of delivering slightly low pressure. It was wired in star and slipping too much, achieving something like 1350 rpm instead of 1425, and it wasn't quite keeping up . The motor itself was completely unharmed.

I would amplify that burnout of the windings with DOL starting is most unlikely. Even large motors can often be started DOL but with unpleasantly high starting currents. A squirrel-cage motor can easily take 5x FLC at standstill, so the above blower example would take upwards of 40A, which would cause the lights sharing the submain to dip visibly (you can just about see the dip with star-delta starting).

The actual starting torques and currents at different voltages depend somewhat on the design and size of the motor, not just on the theoretical ratios. At a standstill the slip frequency is equal to the supply frequency and the rotor cage inductance plays a major part in determining the torque, since the current is seriously out of phase with the stator flux wave. Hence the advantage of rotor-resistance starting over star delta, as this improves the rotor pf as well as limiting the current.
That is an excellent explanation thank you
 

Reply to Star delta motor stuck in star consequences in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi I'm having a problem with a 20 HP pump motor from a hydraulic press to try molds. When we energized the machine, it starts with star...
Replies
8
Views
2K
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock