Hi,

I have a 90KW 3phase electrical motor. It is set up on the star/delta configuration for high current start ups. The problem comes when I start the motor. It is fine in star but when it switches into delta it will trip. It won't trip every time and when it does stay on it will run fine. But stop the motor and try to run it again and sometimes it will trip on delta. I have checked the phase windings,nice low values. Meggered it out- everything ok there. The circuit will switch just fine with no motor connected, so everything brings me back to an overload issue. The thermal OL are set correctly and the supply voltage is coming from a 500KVA Genset. Plenty of power and no problems there. I am in a cold climate so ambient temp is no a problem for over heating. Any ideas??
 
Is the motor getting to speed before it changes to Delta?
Are all bearings, gears etc been lubricated where necessary, this could be a sign of stiffening of workload over time and its taking longer to get to speed in star thus not achieving the changeover speed and taking out the overload device.
 
I'd go with checking the S/D Time first, is it consistent and as above is the motor up to speed before the timer changes to delta?

What load is it driving, has that changed, conveyor, fan?
 
I'd go with checking the S/D Time first, is it consistent and as above is the motor up to speed before the timer changes to delta?

What load is it driving, has that changed, conveyor, fan?

Thanks for your feedback guys. Yes the motor is getting up to speed before the changeover. Timer is set up correctly (20S) the motor is driving a fluid pump mixing brine. I always ensure the operators start the motor offload but the bearings sounds interesting. The humidity is high here and the brine + chemicals are highly corrosive..
 
Hi,

I have a 90KW 3phase electrical motor. It is set up on the star/delta configuration for high current start ups. The problem comes when I start the motor. It is fine in star but when it switches into delta it will trip. It won't trip every time and when it does stay on it will run fine. But stop the motor and try to run it again and sometimes it will trip on delta. I have checked the phase windings,nice low values. Meggered it out- everything ok there. The circuit will switch just fine with no motor connected, so everything brings me back to an overload issue. The thermal OL are set correctly and the supply voltage is coming from a 500KVA Genset. Plenty of power and no problems there. I am in a cold climate so ambient temp is no a problem for over heating. Any ideas??

How old is this Motor? what type of over current protection does the starter have? Have I missed some thing what exactly is tripping?
 
What is motor rated FLC and voltage? What current is the overload relay set at? What current and voltage readings do you get in star and delta just before and after the transition? Is it the overload relay that is tripping the starter off or the circuit OCP?
 
Last edited:

Reply to Star/delta motor trips on Delta in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi Changing a 3 phase star delta motor and replacing with a dol 3 phase motor. Would i be right in thinking I can remove 3 of the 6 cables at...
Replies
3
Views
980
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi I'm having a problem with a 20 HP pump motor from a hydraulic press to try molds. When we energized the machine, it starts with star...
Replies
8
Views
2K
Hello Dear friends, I am going to check a start delta starter for a motor(400KW) which is used for crane and lately it has been causing some...
Replies
1
Views
902

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock