Discuss Strange Fault on a Farm! in the UK Electrical Forum area at ElectriciansForums.net

GJH

-
Reaction score
1
Hi Guys

I am new to the Forum so here goes......

We have been called to a Farm which is 40+ years old, it is a TT 3 phase supply and has a 100mA main RCD switch at the incoming supply.

There is a main DB in the barn and out of that is an SWA sub main which feeds a stable with only one lighting circuit on it. And one 400w SON and weatherproof switch.

We were called out as everytime the light is operated the RCD will trip.After some investigation and testing one of the cables had been chewed which feeds the light as the previous spark had wired it in T&E!

We have replaced the wiring to the switch and light and the light itself is in good working order.

The problem we have is that everytime we operate the light, the incoming SWA gland of the sub main cable will spark and go bang and trip the RCD.
No fuses have blown and the Lines to Neutral and Earth are all clear in the IR test.
I have got 230v from each Line to Neutral and Earth so all seems good.
Not sure what else it can be? - there is no load on the board only this SON fitting and there are no Eddy Current issues.
Does anyone have an idea what it could be?
I can distantly remember a similiar fault when i was an apprentice and im sure it was a loose/partially damaged neutral along the cable?

Thanks in advance for any help on this
 
Bust swa cable somewhere. Is it buried anywhere?
Sounds like the neutral and the armour earth are just about touching.... no fault showing up, but when a big enough load is put on, the return path is trying to use the armour.

40 year old electrics on a farm is unusual. Normally 60 - 70 round these parts.
 
Hi,how is the earthing arrangements of the SWA,incorporated in to the earthing system,at the incomer?
 

Reply to Strange Fault on a Farm! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
540
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
1K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
476
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock