bigspark17

-
Arms
Reaction score
718
Went to see a job where pv pannels have been installed on a large outbuilding, 10mm 3c swa sub ran in to pv isolator/inverter set up, submain supplied off 32A mcb. Seems ok, but the installers left what was already feeding the outbuilding an old 10mm t&e overhead which is now laying on the ground 40m run. My question is could i use the 10mm swa to feed a cu in shed (& shed circuits) then re feed isolator thus leaving the t&e on floor redundant & can be done away with. Loading in the shed is very minimal led strip lights & few general sockets mainly used for shearing once a year. Short of clamping the circuit, how can i veryify i wont overload the circuit. I dont deal with pv as is clear by now im sure. Am i missing something.
 
Within last 6 months! My thoughts too. Cant really see a problem ripping out old t&e sub then feeding pv ac isolator with 32A supply from shed new cu. surely if the panels are producing then wouldn't the shed circuits use this as appose to drawing from grid, or am i wrong?
This is why imo battery bank storage of pv would be possibly more valuable to customer instead of being grid tied.
 
I see no reason why it cannot be reconfigured, you could upgrade the 32A sub supply mcb and resupply from the shed CU. Where is the inverter.
 
I think you should consult the pv installers because if the inverter goes pear shaped they may not uphold any warranty if you have reconfigured the original set up.
 
Good advice @westward10. The pv installers installed the swa new just for the panels in its own trench knowing about the t&e on the floor, the farmer asked them can i get rid of the t&e now but they said no this cable is just for pv,but i suspect as they were on a price they wanted to get in and out! Will post back when i get back to site for a closer look.
 
You may be able to get approval from the installers...but be quick,if they did it 6 months ago,they likely have folded and changed names twice already :rolleyes:
 

Reply to Strange outbuilding/pv set up..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Last year we purchased a home that was built in the late 1990s It has one outbuilding, sort of a barn/shed about 160 feet from the house (and...
Replies
3
Views
1K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock