Discuss Strange readings on ze and zs in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Studio flat recently re-wired.
Ryfields board with main earth coming in and connects to side of ryfields (sealed unit).
Flat’s own head outside has main isolator, from there 25mm tails to inside and then in main switch on DB. With 16mm earth feeding board.

Ze at main switch on DB with main earth disconnected - 0.12 ohms.
Ze At main isolator below head 0.41 ohms with main switch off.

Zs on circuits 0.71 ohms with R1+R2 0.21 ohms.

First question ... how can the ze At the board be greatly lower than at the head isolator with no parallel earths.

Second question... is the ze 0.41, as the Zs of all circuits is going by that result rather than the 0.12?

Help please!
 
Where have you disconnected the main earth, in the dwelling board. Is this main earth definitely connected from the local head or does it derive from the source.
 
Poor/loose connections somewhere.

Also are you using a no trip setting on your MFT?
 
So your main earth goes to a marshalling point before the DB?
 
Hi - my take on what you've said is ...
1. Ze - Zdb = 0.29 Ohms and this is a circuit that's made from a length of 25mm, 16mm, 60A fuse (?) and some connections. How long are these conductors?
2. You've said the external impedance of the Flat's CU is 0.41 Ohms, so this is used in the EIC as Zdb, it's not the Ze as that's at the Ry before the distribution circuit to the Flat.
But I may be completely off track :) .
 
Hi - my take on what you've said is ...
1. Ze - Zdb = 0.29 Ohms and this is a circuit that's made from a length of 25mm, 16mm, 60A fuse (?) and some connections. How long are these conductors?
2. You've said the external impedance of the Flat's CU is 0.41 Ohms, so this is used in the EIC as Zdb, it's not the Ze as that's at the Ry before the distribution circuit to the Flat.
But I may be completely off track :) .
You trying to confuse us:tearsofjoy:
 
What is the supply? if TN-C-S (PME) where is the N-E link Sorry I'm a bit confused upon the setup any pictures?

It’s tns at the main isolator, I can’t tell in regards to the ryfields board as it has a seal. All I can see is a main earth bolted on to the side of the unit. It has baffled me. It is as if in between the isolator and the DB main switch the neutral has found another earth. Which is impossible because I put it in...
 
The Ryefield is likely to be PME internally you will have a common neutral/earth bar. Not always but very often.
 
What is the supply? if TN-C-S (PME) where is the N-E link Sorry I'm a bit confused upon the setup any pictures?

It’s tns at the main isolator, I can’t tell in regards to the ryfields board as it has a seal. All I can see is a main earth bolted on to the side of the unit. It has baffled me. It is as if in between the isolator and the DB main switch the neutral has found another earth. Which is impossible because I put it in...
 

Reply to Strange readings on ze and zs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
493
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
840
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock