Strange/Unusual Fault

Discuss Strange/Unusual Fault in the UK Electrical Forum area at ElectriciansForums.net

mattg4321

-
Esteemed
Arms
Reaction score
2,046
So there I was the other day posting on here about me going to solve faults others couldn't find and I've got one myself.

It's been a while since I've been stumped but I am now.

Symptoms - gate supply keeps tripping (when it's raining according to customer). There's a 6mm 3 core SWA running about 3-400m (yes you read that right), to a cabinet by the gates where there is a double socket inside feeding a right mess for the gates. Protected by Hager reduced height 20A RCBO.

Unplugged both sockets, IR tested cable from consumer unit to double socket.

L-N = 140Mohm
L-E = 71Mohm
N-E = 70Mohm

IR tested the plugs for the gate controls. L&N together to earth. One was 12Mohm, the other was 299Mohm. Throughout all the below I never plugged the gates back into the double socket.

With the plugs still unplugged and nothing in the double socked I went to turn on the RCBO. Took 4 goes to get it to stay in. No bang, just as if there was N/E fault there. 1/2 trip and ramp tested RCBO and both returned no result as it tripped so early/quickly. Removed outgoing cables from RCBO and all tested well - 23mA ramp test and turned on without any trouble.

Changed RCBO to rule that out and same symptoms.

Tested IR a few more times to make sure and same results. Tested outgoing cables to socket to all other cables in consumer unit to see if anything was mixed up. All good. Physically traced cables in consumer unit to check same and again all good.

I'm guessing it's something to do with the length of the cable? I can only guess that somehow I'm losing current from the line to the earth as they are run alongside eachother for such a distance? This doesn't really make sense to me though. Someone put me out of my misery!
 
So there I was the other day posting on here about me going to solve faults others couldn't find and I've got one myself.

It's been a while since I've been stumped but I am now.

Symptoms - gate supply keeps tripping (when it's raining according to customer). There's a 6mm 3 core SWA running about 3-400m (yes you read that right), to a cabinet by the gates where there is a double socket inside feeding a right mess for the gates. Protected by Hager reduced height 20A RCBO.

Unplugged both sockets, IR tested cable from consumer unit to double socket.

L-N = 140Mohm
L-E = 71Mohm
N-E = 70Mohm

IR tested the plugs for the gate controls. L&N together to earth. One was 12Mohm, the other was 299Mohm. Throughout all the below I never plugged the gates back into the double socket.

With the plugs still unplugged and nothing in the double socked I went to turn on the RCBO. Took 4 goes to get it to stay in. No bang, just as if there was N/E fault there. 1/2 trip and ramp tested RCBO and both returned no result as it tripped so early/quickly. Removed outgoing cables from RCBO and all tested well - 23mA ramp test and turned on without any trouble.

Changed RCBO to rule that out and same symptoms.

Tested IR a few more times to make sure and same results. Tested outgoing cables to socket to all other cables in consumer unit to see if anything was mixed up. All good. Physically traced cables in consumer unit to check same and again all good.

I'm guessing it's something to do with the length of the cable? I can only guess that somehow I'm losing current from the line to the earth as they are run alongside eachother for such a distance? This doesn't really make sense to me though. Someone put me out of my misery!

I'd be surprised if that could cause enough current to flow to trip an RCBO. 15mA+ just by the coupling of adjacent cables?
 
Is it a metal double socket?
What I don't think you've mentioned is taking front off double socket, but see exactly what you mean about the mix of IR tests and RCBO tripping.
Is it an RCBO with a functional earth connection?
 
Yes, capacitive leakage is a thing and on long cables it's an important thing. This case looks borderline.

Manufacturers don't usually publish capacitance for small LV power cables in their data, but at some point I clearly managed to get data for 2.5mm SWA as I wrote about it in this thread (although did not include the link mentioned there):

My figure of 0.25μF/km was for one core to all the others, whereas with a 3-core on single phase, leakage to the neutral core does not create residual current, so the effective L-E capacitance for our purposes is somewhat lower. However, the cable here at 6mm² has conductors of larger surface area but probably not spaced proportionately further apart, so the capacitance per metre will be higher.

If we took a wild guess at 0.3μF/km L-E effective, the cable will contribute
230 * 2 * pi * 50 * 0.3^e-6 = 22mA of leakge per km

Hence 22 * 350 /1000 = 8mA for a 350m cable (very roughly, since we don't have the actual capacitance for that cable size). That is the leakage at 50Hz, however, when closing the RCBO on the peak of the mains waveform, the fast risetime voltage step might pass a big enough slug of charge to earth to trip the RCBO straight back off. The leakage might be somewhat higher due to harmonics and noise on the supply, too, as the capacitance to earth tends to filter them off. I could imagine a situation where switching large loads on the same supply caused spikes of many mA through the cable capacitance.

If the customer is correct that it trips more when raining, there might be moisture ingress into the cable which, if it surrounds the line core insulation, further increases the capacitance. Alternatively, the tripping when already energised might be a combination of capacitive and resistive leakage (from other causes), while the difficulty resetting is due to the transient voltage across the capacitance.

100mA RCBO at the source for fault protection and 30mA at the destination for additional?
 
L-N = 140Mohm
L-E = 71Mohm
N-E = 70Mohm
I'm thinking out loud here...
Assuming armour is earthed both ends.
With E and armour earthed you have same effect as a shorter cable and reduced (normal) resistance.
IR is inversely proportional to the cables length.

All that to say shouldn't the IR measurements involving E be higher than the L to N reading?
EDIT - ^^complete rubbish^^ penny has dropped now....
 
Last edited:
I don't follow you, but the individual resistances core-core and to SWA are governed by the bulk resistivity of the insulation and filler materials, and the area and thickness of each. With the large area of SWA in contact with the filler, and this not necessarily having high insulation properties, one might expect the resistance from each core to be lower to the SWA than to another isolated core, since only one layer of insulation is involved instead of two. If the CPC core is strapped to the SWA, I would expect results much as the OP has measured.

OTOH, these resistances are all up in the 'ignore' category. They would need to be a thousand times lower to be playing any significant role in the RCBO tripping.
 
With the large area of SWA in contact with the filler, and this not necessarily having high insulation properties, one might expect the resistance from each core to be lower to the SWA than to another isolated core
Thanks. That was the main detail I didn't take into account at all. It was also completely illogical to compare normal resistance changes due to csa with the general rule of IR getting shorter as a cable gets shorter. Total brain fail really!
 
does the circuit need any rcd at source end at all? Armoured cable

Maybe not. Top of head on a B20 2 cores or XLPE cable with armour alone are out, but 3rd core + armour are OK. Probably doesn't need to be 20A anyway.
 
This is an existing installation right, that has been working satisfactorily for years and just developed a fault?

Cable capacitance is a plausible cause of leakage but if the circuit has been fine for a while/years I'd be looking elsewhere, has there been any work (fence posts!) along its route? Have you tested it while its raining (or just after)?
 
It's a valid point, and my hunch in post #8 was that there might be leakage contributions from the capacitance (mainly causing the difficulty resetting) and damp (causing the tripping during rain as mentioned by the customer).

Though I would find it surprising for cable with insulation damage underground to recover from the tens of kilohms needed to cause a trip, all the way to 70MΩ L-E as measured by the OP. Plus the L-E and N-E readings are identical and the L-N double the resistance, which is fairly convincing. The IR of one of the gate systems was much lower at 12MΩ.

The factor that suggests to me that capacitance is at least a significant player here is that both the original and replacement RCBOs tested fine on their own, and the cable tested fine at 70 - 140MΩ, but as soon as the cable was connected to the RCBO it became difficult to reset. I.e. the effect was apparent at the same time as the cable was showing good insulation, regardless of whether the insulation always remains good.

History is increasingly of interest. How old is it? When did it start tripping?
 
It was extremely wet here today, so I doubt rainfall will take the IR any lower than that found.

Customer has just moved in a few months ago. It’s tripping intermittently since they moved in. Consumer unit was changed early this year. Very plausible there would’ve been no rcd on the gate circuit beforehand.

I really don’t think there is any other realistic explanation than lucien’s. I was on those lines myself, but wasn’t sure if that was realistic. To be honest I’ve not come across this before. But I’ve also not come across a final circuit 400m plus in length that I can remember!
 
might be an idea to use an earthleagage clamp meter ( a decent one). once or twice i've had tripping issues and IR tests have been in the 100s of Megs. sometimes a IR test just will not show up a fault, esp. if it's a slight water/damp ingress. if the SWA does not need RCD protection (regs. wise), feed from a non-RCD way.
 
Can one buy a single length of 6mm2 swa 400m long?
Yes, most wholesalers will order it in for you.

in general I would not expect any issues until about 1km
if I remember right, you can have about 4 tonne on a large reel, after that it would be more difficult to obtain.
 
I would be inclined to move the RCD to the gate location, even install an IP rated board with 2-3 RCBO's, then each socket would have an individual RCD

I know that they are phasing out RCD sockets but that is also an option at the gate end

Are they phasing out RCD sockets?
 
if the SWA does not need RCD protection (regs. wise), feed from a non-RCD way.
Agreed. I think the issue's going to be ADS for the cable, with Zs of 4 ohms, unless the load is light enough for a B6 breaker, or even 10 amp BS88 fuse, it looks to me like it's going to need an RCD at source for fault protection.
 
It’s bad practise to add RCD to comply with ADS ,this would not work on a Line-Neutral fault . This would be a departure from the regulations which does not improve safety , its better to run a bigger cable or parallel cables or even an extra R2 (cpc)
 
It’s bad practise to add RCD to comply with ADS ,this would not work on a Line-Neutral fault . This would be a departure from the regulations which does not improve safety , its better to run a bigger cable or parallel cables or even an extra R2 (cpc)
I agree in ideal circumstances but we are not talking about adding one, we are talking about the effects of removing one. The original design which the OP has inherited is not ideal, and far from easy to change. It’s likely questionable with regard to volt drop too.
In any case I’m fairly sure it is in fact permitted to have an RCD for fault protection and separate overload protection as per reg 411.4.5
 

Reply to Strange/Unusual Fault in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock