I have an installation that I maintain and the DNO have recently changed their pole transformer. Since this change I have been unable to do earth loop tests. The supply comes from a HV to LV transformer and there is a HV earth rod right next to the neutral/earth rod for the HV to LV transformer.

The installation is a TT system with one earth rod. For some reason I get 186V L-E and 66V N-E and 252V L-N at the cut out fuse when the fuse and the neutral are removed.

Could it be stray voltage from the HV system?
And why would this not give me an earth loop reading on my tester?

Thanks in advance
 
It's not giving you a EFLI as Uo is 186v as is below testers parameters.

If you are really getting those readings at the origin if supply then phone DNO asap

** edit ** Dave beat me to it!
 
I have an installation that I maintain and the DNO have recently changed their pole transformer. Since this change I have been unable to do earth loop tests. The supply comes from a HV to LV transformer and there is a HV earth rod right next to the neutral/earth rod for the HV to LV transformer.

The installation is a TT system with one earth rod. For some reason I get 186V L-E and 66V N-E and 252V L-N at the cut out fuse when the fuse and the neutral are removed.

Could it be stray voltage from the HV system?
And why would this not give me an earth loop reading on my tester?

Thanks in advance
What HV system are you referring to SJE?
 
The installation is a TT system with one earth rod. For some reason I get 186V L-E and 66V N-E and 252V L-N at the cut out fuse when the fuse and the neutral are removed.

Are you sure it's TT and not PNB (TNCS), is this the only installation fed from this pole mount transformer?
The reason I ask is that if you are disconnecting things from the DNO's cutout, which you are obviously not allowed to do, you could have caused this dangerous condition if it is PNB.
 
Are you sure it's TT and not PNB (TNCS), is this the only installation fed from this pole mount transformer?
The reason I ask is that if you are disconnecting things from the DNO's cutout, which you are obviously not allowed to do, you could have caused this dangerous condition if it is PNB.

I have had the DNO out to investigate and they removed the cut out and neutral for me. Also, yes we are the only connection to the transformer.
 

Reply to Stray voltage in Neutral - help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
691
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
679
If we had 4 appliances to power, one in every room of a house, Once the current passes through them all, the remaining voltage & current is said...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock