Discuss Street lighting testing!!! Help !! in the UK Electrical Forum area at ElectriciansForums.net

O

ooMARK84oo

Hi all ,

i am am about to be starting with a new firm who insist on all electrical test s to be done on each column with a new lantern. Could anyone help me with the procedure of these test and exactly how to perform them as I know they would differ from a domestic testing .

Any help appreciated

Mark
 
Well you can't really do much more than IR tests L+N to earth if you're talking about the actual light columns!! What other tests does this new company want you to conduct?
 
Still a circuit off a db isnt it? (feeder pillar?)

Boydy
Yes it is from a feeder pillar .
i am just slightly confused as to when doing IR it will affect
the gear at top (LED lantern).
they also want contuity
EFL
POLARITY (speaks for itself)
ZE
ZS
Again if anyone can help in detail how to perform all these from base of column would be great .
 
I think you need clarification on whether you are testing the supply circuit only or they require you to test the flex between the cutout and the gear tray. This would obviously have been best done when these new lights were installed if the post drops require testing.
 
Hi Andy ,
they are new lanterns and it is the flex between cutout and lantern being tested . I am reasonably new to this as still learning at college.
 
I have actually done HEA inspection and testing course but was over a year ago and never done any testing since . Just after bit of advice really and refreshing . Thanks
 
You are gonna need to be at the top of the post then aren't you ? If you have technical knowledge or confidence issues you really should be going to your boss and asking for guidance or supervision due to your lack of experience.
 
If IR testing is conducted L+N to earth then it shouldn't be a problem. As i stated before trying to conduct other tests between incoming cables at the base of the lampost and the lampost lamp is insane, unless you have equipement to reach the lamp position.


EFLI and Zs is the same thing, where (at what position(s)) are you intending to conduct this/these tests? Ze is only taken at the point of the incoming DNO supply, which may not be at the Feeder Pillar supplying the string of street lighting posts... In which case the feeder pillars Zs will effectively become Zdb.


If you're talking about testing at every lampost with regards to supply cables from feeder piller to each lamposts connection point, then fine i can understand that. As has been stated, conduct the same tests as you would normally for any circuit. Just remember to disconnect/isolate the cable to the LED lamp during IR testing of supply cables...
 
Hi Andy ,
they are new lanterns and it is the flex between cutout and lantern being tested . I am reasonably new to this as still learning at college.

Bloody ridiculous!!

Do any dead tests before post is erected. Personally i wouldn't bother past a L+N to E, IR test once everything's connected as far as the internal flex is concerned!!
 
street lighting testing crash course
==========================

after replacing a light fitting on an existing lamp post you are required to carry out a "unit test"

this comprises of

L&N to E insulation resistance test on the lantern flex
ELI test at the cut-out ( record as Ze if dno supply , record as Zs if private supply )
visual confirmation that earth bonding to the post ( if metal ) is satisfactory
visual confirmation of correct polarity
visual confirmation of correct size fuse / mcb

thats it really.
 
Last edited by a moderator:
ELI test at the cut-out (record as Ze if dno supply, record as Zs if private supply)

Not sure what you mean here, are you talking about the cut out fuse at the lampost or at the supplying feeder pillar (or whatever)?? If at the lamppost, that isn't going to be Ze, it'll be Zs.
Ze is recorded once at the origin of the supply, be it DNO or Private supply.
 
Not sure what you mean here, are you talking about the cut out fuse at the lampost or at the supplying feeder pillar (or whatever)?? If at the lamppost, that isn't going to be Ze, it'll be Zs.
Ze is recorded once at the origin of the supply, be it DNO or Private supply.

street lights can have either a private supply , usually swa from a feeder pillar , or its own mini 25A dno supply & cut-out.
hence my distinction between Ze or ZS when recording the reading on a cert.
 

Reply to Street lighting testing!!! Help !! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
637
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
634
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
639
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
390

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock