Search the forum,

Discuss Sub Main and seperate earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
55
If I'm running two core 25mm SWA as the submain with a 16mm (non-armoured) earth seperately then will the earth require its own mechanical protection?

Also as regards earthing the armour wire - will 6mm (from the tag to the earth block) be sufficient as it now counts as extraneous metalwork?
 
The armours alone are more than ample. Just use a short amount of you’re 10mm for each end of the armours and save the rest for the next job.

Waste of money.
 
I generally use armourings if i am designing BUT i have come across two industrial sites and at least one main contracting company that thought i was some kind of lunatic for suggesting such a think. Where earth is run alongside the supply SWA it needs to follow same route, easiest is to tie wrap it to the supply cable. Mechanical protection not mandatory but make a judgement call on the environment.
 
Also, with regards to the armour of the SWA, if you intend not to use this as an earthing conductor (not sure why you would do this unless the DNO has specifically stated no exporting of their PME) if this is terminated correctly at both ends then the armour is neither an exposed or an extraneous conductive part and as such does not 'need' earthing or bonding although highly preferable, but, if you intend for it to be buried in the ground it will need earthing (ideally at the supply end) as per 522.6.100 and if you intend for it to be buried in a wall at a depth of less than 50mm then it will need earthing as per 522.8.10. Carrying out an adiabatic equation will confirm the size of the CPC needed to earth the armour.
 
Last edited:
Also, with regards to the armour of the SWA, if you intend not to use this as an earthing conductor (not sure why you would do this unless the DNO has specifically stated no exporting of their PME) if this is terminated correctly at both ends then the armour is neither an exposed or an extraneous conductive part and as such does not 'need' earthing or bonding although highly preferable, but, if you intend for it to be buried in the ground it will need earthing (ideally at the supply end) as per 522.6.100 and if you intend for it to be buried in a wall at a depth of less than 50mm then it will need earthing as per 522.8.10. Carrying out an adiabatic equation will confirm the size of the CPC needed to earth the armour.

(if this is terminated correctly at both ends then the armour is neither an exposed or an extraneous conductive part and as such does not 'need' earthing or bonding ).

Hi mate....... I'm a bit confused with the above statement.
Are you saying that because the Swa has an outer sheath and will be shrouded at both ends then it negates the necessity to earth it?
I'm always willing to learn but would have thought it was always an exposed conductive part and would need earthing ( which it would be if it was terminated correctly at both ends surely?).
An internal /external cable fault would need the armour to be earthed would it not?
Sorry if I'm having a 'blonde moment' lol
 
The only reason i can see for using a separate earthing/bonding conductor is if your extending a PME system outside of it's home equipotential zone, (eg, where extraneous services etc are going to be present) as the SWA will not comply with bonding CSA. But in that case, i would useing a 3 core SWA cable, the cost will be off-set by the time it's going to take you fluffing about running a separate 16mm single earthing/bonding conductor and tying it to the SWA cable!!
 
(if this is terminated correctly at both ends then the armour is neither an exposed or an extraneous conductive part and as such does not 'need' earthing or bonding ).

Hi mate....... I'm a bit confused with the above statement.
Are you saying that because the Swa has an outer sheath and will be shrouded at both ends then it negates the necessity to earth it?
I'm always willing to learn but would have thought it was always an exposed conductive part and would need earthing ( which it would be if it was terminated correctly at both ends surely?).
An internal /external cable fault would need the armour to be earthed would it not?
Sorry if I'm having a 'blonde moment' lol

It is possible to terminate SWA in compliance with 134.1.4 without using glands (why anyone would do so I don't know, but it can be done) in which case the armour would not need earthing, also, if connected with appropriate glands and then shrouded, then you are correct, the armour would still not need earthing. That is unless you are burying your cable underground or in a wall at a depth of less than 50mm.

Some may even argue that because a steel wired armour cable contains within its armour conductors that are housed in basic insulation which are in turn then sheathed that the inner part of the cable meets the requirements for both basic and fault protection therefore meaning that the armour cannot be by definition an exposed conductive part.

I am by no means advocating not terminating and glanding SWA in accordance with the standard of widely known best practice, I am merely stating that the armour is arguably neither an exposed or extraneous conductive part meaning that unless specifically required, does not need earthing or bonding.
 
Last edited:
"I am by no means advocating not terminating and glanding SWA in accordance with the standard of widely known best practice, I am merely stating that the armour is arguably neither an exposed or extraneous conductive part meaning that unless specifically required, does not need earthing or bonding".

I now your not mate but there would be no need to use Swa if you weren't going to gland it surely?
What would be the point...........mechanical protection !!
The cable then gets damaged and you have a phase ( or line lol ) fault to the armour but it isn't earthed?

IMO the armour is an exposed conductive part as its part of the system and always will be and therefore needs to be earthed.
That's the way I do it anyway lol.
How can it 'not' be an exposed conductive part?
If someone puts there spade or digger through it you would want it earthed surely?
 
I now your not mate but there would be no need to use Swa if you weren't going to gland it surely?
What would be the point...........mechanical protection !!

I totally agree!

IMO the armour is an exposed conductive part as its part of the system.

Being part of a wiring system doesn't neccessarily make it an exposed conductive part. Look up the definition in Part 2.

If someone puts there spade or digger through it you would want it earthed surely?

That's exactly why 522.6.100 calls for it to be earthed if buried. That still doesn't make it an exposed conductive part though.
 

Reply to Sub Main and seperate earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock