Currently reading:
Sub Main Zdb Test

Discuss Sub Main Zdb Test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
0
Hi, this is my first post here.

I have a 3 phase board with a 40amp circuit breaker supplying a single phase board to a small office.
I understand that with the 3 phase board how to get the Ze thats not an issue. How do I test to get my Zs (Zdb) for the single phase board?

Do I link the L&E together in the 3 phase board and then test between L&E on the main breaker for the single phase board? This will give me a Zs then i add this to the R1 + R2
I want to get a reading for my Ze at DB for my sub main board on the EICR

Thanks
 
Use an earth fault loop impedance tester, you measure Zs at the single phase office board. No different to any other circuit.
 

Reply to Sub Main Zdb Test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock