Discuss Suggestions for frost protection stats in the Central Heating Systems area at ElectriciansForums.net

Simon47

-
Esteemed
Arms
Supporter
Reaction score
1,282
At our church, one of the things I've done is sort out the heating wiring (as best I can for now). The schematic is as shown below.

The theory that had me arrive at this goes :
Previously, when the wall stats was satisfied, the pump stopped along with the boiler. As we have a number of fan-coils, they quickly ran out of heat in their small water volume, and the place would go cold quite quickly. By adding pump over-run, the water still flows, the fan coils (if still on) can put out heat, and we use the stored heat in (by my guestimate) about 100 gallons of water until the wall stats brings the boiler back on again.

When I first got involved, there was a frost stat, but thankfully it didn't work as it was wired to simply bypass the timer and wall stats - thus heating the church all the time the air temperature outside was very low. It's a "big barn with lots of single glazing and gaps" so takes a considerable amount of oil to heat it.
So as well as replacing the frost stat, I added a pipe stat so the boiler would only run until the pipes are lukewarm - not enough to turn on the fan coils (now I've changed their pipe stats to a higher temperature) or to put too much heat out through the old "massive pipes" radiator system. By running the pump more than it perhaps needs to, it minimises the risk of any cold spots in the system - the stats can only measure the temperatures at single points.

Wiring Diagram 2.png
But there is a problem. Both the frost and pipe stats (Honeywell T4360 frost stat, L641B pipe stat) operate at too high temperatures and thus we burn more oil than is needed. Both are turned down to minimum.

From memory, I've seen the frost stat demanding when my car had told me it was 8˚C outside - and it's in the boiler room so should be a bit warmer than outside anyway). That in itself isn't too bad as it simply turns the pump on, and while it can burn through lecky, it's not half as bad as running the oil burner when it's not needed. Spec says "3 to 20°C setpoint range".

The pipe stat is a problem. It turns on at 10˚C and doesn't turn off until it reaches 20˚C - which means it's running the system warmer and for longer than is needed. The spec said (seems to have gone off their site now) "L641B1004 Controller, setting 10 to 40 ̊C, min. setting 2°C"

I did try having a conversation with Honeywell, but the response I got from them was basically "not wired right, wire it this way" while totally ignoring the actual issues, and I never got any further replies from them. It was obvious that I was dealing with someone who could only look at they examples, see that my wiring didn't match, so couldn't cope with any further discussion - you can tell it's going to be interesting when somsone doesn't see any reason you might not want to backfeed a control circuit 🙄 Neither of the stats is shown as having an accelerator heater according to their spec sheets, so it shouldn't matter which way through them the current flows.

So, anyone else had similar issues ? How did you deal with it ? Does anyone make stats that work as advertised ?



A few more ramblings on the design.
As an engineer rather than just a "wiring by numbers" person, it "just isn't right" to backfeed a circuit when it's avoidable. Apart from that, at some point I want to alter the time clock & wall stat arrangement - and when I figure out access routes, I will probably power (or at least control) the fan coils from the timer/wall stat section. By not backfeeding the controls, that avoids having the frost protection turn on the fan coil fans - without needing am extra relay to isolate them.
 
Probably to late but I recently moved to a house with the same pipe stat and also found the minimum setting to high. Took it apart & found the whole thing was as if the wrong base unit had been mated with the wrong top as the operating range was more like a cylinder stat. To fix it I chopped a short length of the microswitch operating pin & re-calibrated the wax covered screw that has the square nut holding the bi-metalic strip and tested it using indoor/outdoor air temperature and a DVM. Result it is now operating at ~12C that is plenty enough to stop pipes freezing.
 
Actually, not too late as I've not had chance to revisit this issue since. I guess since we're getting into colder weather I ought to ...
 

Reply to Suggestions for frost protection stats in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

So I’ve been having this issue with my boiler for a while now, I’ve currently got one stat in the hall that when I turn it on it brings the...
Replies
4
Views
672
Hi all, I've noticed that my UFH pump is not always turning on as soon as the stat & valve calls for heat. This results in hot water passing...
Replies
8
Views
626
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
951
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
Hi guys, Do you know if I can install a Nest E with the heat link in the airing cupboard as opposed to the room stat position? System is a S plan...
Replies
1
Views
716

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock