Discuss Suitability of SWA armouring as CPC in the UK Electrical Forum area at ElectriciansForums.net

IAmSparkytus!

-
Esteemed
Arms
Reaction score
315

Anyone know how reliable the tables on this website are for determining whether the armouring of a cable can be used as it's earth?

Not too sure how old the page of the website is so could have changed since it was made or could have been wrong to start with I suppose

TIA
 
I don't get it flagged as dodgy, but maybe my standards are lower...

It reminds me of something I read a while back, probably an IET article or publication. the page says last updated 2012 so not quite current, even though most of the factors remain the same.
 

Anyone know how reliable the tables on this website are for determining whether the armouring of a cable can be used as it's earth?

Not too sure how old the page of the website is so could have changed since it was made or could have been wrong to start with I suppose

TIA

That table has been knocking around in various forms for years and is based on the simplified calculation of CPC size. As a result it will be correct where it says that the armour is a suitable size, but if you calculate using the adiabatic equation you will find that where the table says the armour is unsuitable it is in actual fact almost always suitable.

This all assumes the armour is only being used as a CPC and is not required to also be a main bond, in which case it will almost certainly be unsuitable.
 
Nope, checked again and for 90C thermosetting k1 is 100 from Table 43.1 and k2 is 46 from Table 54.4 so here are the values I get, assuming those k values and assuming Fe is 8 times poorer than Cu for conductivity:
Live Cu​
Min CPC Cu Table 54.7​
SWA adiabatic eq 54.7​
CPC PME Table 54.8​
PME SWA​
1.5​
1.5​
3.3​
10​
80​
2.5​
2.5​
5.4​
10​
80​
4​
4​
8.7​
10​
80​
6​
6​
13.0​
10​
80​
10​
10​
21.7​
10​
80​
16​
16​
34.8​
10​
80​
25​
16​
34.8​
10​
80​
35​
16​
34.8​
10​
80​
50​
25​
54.3​
16​
128​
70​
35​
76.1​
25​
200​
95​
47.5​
103.3​
25​
200​
120​
60​
130.4​
35​
280​
150​
75​
163.0​
35​
280​
185​
92.5​
201.1​
50​
400​
 
Last edited:
What you see is the PME main bonding cases is far more demanding, basically as it might be carrying tens or hundreds of amps for hours under open-PEN fault conditions and is not met by any of the SWA cable construction. So it is really a case of external CPC in parallel, or use an extra core in the SWA if that is the means by which any bonding is returned to the DNO connection point.

EDIT: Also note the extra note in 544.1.1 with AM2 about cables to other building not having to be fully to this in some cases.
 
Nope, checked again and for 90C thermosetting k1 is 100 from Table 43.1 and k2 is 46 from Table 54.4 so here are the values I get, assuming those k values and assuming Fe is 8 times poorer than Cu for conductivity:
Live Cu​
Min CPC Cu Table 54.7​
SWA adiabatic eq 54.7​
CPC PME Table 54.8​
PME SWA​
1.5​
1.5​
3.3​
10​
80​
2.5​
2.5​
5.4​
10​
80​
4​
4​
8.7​
10​
80​
6​
6​
13.0​
10​
80​
10​
10​
21.7​
10​
80​
16​
16​
34.8​
10​
80​
25​
16​
34.8​
10​
80​
35​
16​
34.8​
10​
80​
50​
25​
54.3​
16​
128​
70​
35​
76.1​
25​
200​
95​
47.5​
103.3​
25​
200​
120​
60​
130.4​
35​
280​
150​
75​
163.0​
35​
280​
185​
92.5​
201.1​
50​
400​
The end list… is it for the swa used for that circuit..16mm being 80 mm & confirms that the armouring is compliant
 
The end list… is it for the swa used for that circuit..16mm being 80 mm & confirms that the armouring is compliant
No, it means if the SWA armour is your main bond for PME situations it needs to be 80mm section to match 10mm copper as specified in Table 54.8. That is only met for big cables such as (I think) 35mm 4C, 50mm 3C, and 70mm 2C or larger. That 10mm PME requirement is why often folks use 10mm 3C for an out-building with extraneous parts as then the copper CPC meets it.

The PME size I used is based on the incoming cable with Table 54.8, for a sub-main you might well have much larger conductors if the length is significant just to meet VD.

But under AM2 there is some relaxing of that if its a sub-main to other buildings in a group but would need to read the details of it.
 
Last edited:
No, it means if the SWA armour is your main bond for PME situations it needs to be 80mm section to match 10mm copper as specified in Table 54.8. That is only met for big cables such as (I think) 35mm 4C, 50mm 3C, and 70mm 2C or larger. That 10mm PME requirement is why often folks use 10mm 3C for an out-building with extraneous parts as then the copper CPC meets it.

The PME size I used is based on the incoming cable with Table 54.8, for a sub-main you might well have much larger conductors if the length is significant just to meet VD.

But under AM2 there is some relaxing of that if its a sub-main to other buildings in a group but would need to read the details of it.
Thank you understand now the poor conductivity of the armouring.
 
But under AM2 there is some relaxing of that if its a sub-main to other buildings in a group but would need to read the details of it.
There is a whole thread about this, also started by @cliffed , the conclusion of which was that this amendment applies only where PME conditions do not apply.

 
Nope, checked again and for 90C thermosetting k1 is 100 from Table 43.1 and k2 is 46 from Table 54.4 so here are the values I get, assuming those k values and assuming Fe is 8 times poorer than Cu for conductivity:
Live Cu​
Min CPC Cu Table 54.7​
SWA adiabatic eq 54.7​
CPC PME Table 54.8​
PME SWA​
1.5​
1.5​
3.3​
10​
80​
2.5​
2.5​
5.4​
10​
80​
4​
4​
8.7​
10​
80​
6​
6​
13.0​
10​
80​
10​
10​
21.7​
10​
80​
16​
16​
34.8​
10​
80​
25​
16​
34.8​
10​
80​
35​
16​
34.8​
10​
80​
50​
25​
54.3​
16​
128​
70​
35​
76.1​
25​
200​
95​
47.5​
103.3​
25​
200​
120​
60​
130.4​
35​
280​
150​
75​
163.0​
35​
280​
185​
92.5​
201.1​
50​
400​

In your column headings I think that the third column should be selection in accordance with table 54.7 and not adiabatic equation shouldn't it?
 
In your column headings I think that the third column should be selection in accordance with table 54.7 and not adiabatic equation shouldn't it?
It is badly explained in my post but by "adiabatic eq" I meant the adiabatic equivalent conductor to the copper one.

So from Table 54.7 it has you list of CPC=line to CPC=line/2 sizes, and then the suggestion that for fault handling equivalent using other types of material you scale the size by the ratio of the two adiabatic k-factors (k1 & k2). This leads to a conductor that has the same short-term overload handling as it takes in to account both the higher resistance of other conductors like steel, but also that as you make the conductor bigger to reduce that resistance penalty, it also increases the heat-absorbing capacity.

If the only difference was material resistance, and not any other thermal factor, then you would need the square root of the conductivity bigger. For example, if you had a poor copper version that was identical to copper in every way but it had 4 times the electrical resistance, but time you make it sqrt(4) = 2 times larger to drop the resistance to only double the normal copper resistance, you also have double the metal to adsorb the energy and so you reach the same post-fault temperature form given I2t. If it was 9 times less conductive then by time you make the CSA 3 times bigger you have 3 times the I^2R heating but also 3 times the mass, etc, etc.

That is far less of a problem than the open-PEN fault case where the CPC has to sustain a given high current to whatever is bonded (say metal service pipes back to the substation via another TN-C-S bond) as then your temperature rise is given only by I^2R and the thermal environment of the cable. So to make steel armour run at the same ultimate temperature as a copper CPC you need its R to be the same (more or less, a larger cable will generally dissipate heat better as more surface area) so instead of the k1 & k2 values being used you are looking at the material resistivity, which is about 8 times instead of the k-factors of 100/46 = 2.17
 
Last edited:

Reply to Suitability of SWA armouring as CPC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
Replies
7
Views
1K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
A recent discussion on conduit choice wandered over to pros and cons of the 'conlok' style and a link was posted to one of the Efixx videos in...
Replies
29
Views
4K
I’m wavering a bit on this one. RCD then B10 breaker. 1.5 sq mm 3 core SWA. That runs underground in ducting, then up and feeds about 10 LED class...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock