    DOWNHAM MARKET
    been asked to price a socket to a Summer house , throwing it out their for any views which may help me decide my course of action , Ideally i would like to get back to the Consumer unit , but its virtually impossible without major structural upset , and can not go external from it either due to the nature of the property . So , what i do have is a Garage Socket , which i am assuming is from the current ring main , on a spur . I thought maybe fitting a fused spur into the line and going off the socket down to the Summer House which is approx 25-30 meters away and feed a socket for a reading light and small heater , problem is the distance and what amps i would have at the Summer house already from a spur , plus the size of SWA i would need , seems a mighty job for a Summer house which could not get further away from a source which is so hard to get to . Any Views ?
     
    • Bad Spelling Bad Spelling x 1
    • Dumb Dumb x 1
  2. KevinH
    Offline

    KevinH Active EF Member

    Location:
    Pembrokeshire
    Business Name:
    K H Electrical
    Bit worried someone asking these sort of questions are willing to carry out a job that requires notification. A registered sparky would carry out simple cable calcs to work out cable size AND identify where garage socket is fed from.
    If you suspect the garage socket is fed by a spur off the ring main, why would you need another spur in line?
     
    • Agree Agree x 3
  3. Spoon
    Offline

    Spoon Forum Mentor

    Location:
    Lancashire
    I'm with @KevinH@KevinH post above.
    You want to spur off a spur and run it 30 meters from a circuit that that you are not sure about.????
    Please clarify you post mate.....
     
    • Like Like x 1
  4. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    Ditto on the agreement front.

    Lets take a big step backwards...what would you want to power in this hut?

    (PS, I hate the word assume.)
     
  5. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    I'm with Kevin and Spoon.
     
    • Like Like x 1
  6. WELLSIANA
    Offline

    WELLSIANA EF Member

    Location:
    DOWNHAM MARKET
    already i laugh , it was just thoughts , just asking views , and sorry no i do not crawl about in lofts to determine where a cable goes , but my assumption is the garage socket is spurred off the ring main like most extra sockets get done , of course i would check if i went any further , it is not already on a spur as in 13amp fused spur . I know full well i can ring up technical if needed but was merely asking views , as for certification hahaha , not many carry that out around here only the big boys , everyone misses that part of the job and saves a fortune ha ha wink
     
    • Dumb Dumb x 12
    • Dislike Dislike x 1
  7. Archy Styrigg
    Offline

    Archy Styrigg Forum Mentor

    Location:
    Manchester
    I'm with Kevin, Spoon, Pete AND Taylor :)
     
    • Agree Agree x 2
  8. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    OK. Lets try again

     
  9. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    With what TTC?
     
  10. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    I asked what the estimated load might be. You may recall that we start cable calculations with the answer to trivial issues like that!
     
  11. KevinH
    Offline

    KevinH Active EF Member

    Location:
    Pembrokeshire
    Business Name:
    K H Electrical
    OP laughs about not certifying work in his area to "save a fortune"......no laughing matter I'm afraid....that's how buildings burn and people get killed!
     
    • Agree Agree x 6
    • Like Like x 2
    • Optimistic Optimistic x 1
  12. Spoon
    Offline

    Spoon Forum Mentor

    Location:
    Lancashire
    Not a lot we can say mate.
    From your general outlook on things it looks like you will do whatever you want to do.
    Crack on.....
     
    • Like Like x 3
    • Funny Funny x 1
  13. Andy78
    Online

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    I think the OP is on a wind up. Either that or the electrical installations in Downham Market are decidedly down market.
     
    • Agree Agree x 6
  14. Grezza
    Offline

    Grezza Active EF Member

    Location:
    Liverpool
    Wowzer. Where do I begin??!
     
    • Like Like x 1
  15. DPG
    Offline

    DPG Respected Member

    Location:
    S Yorkshire
    This is one of the best lines I have read for a while:

    ...problem is the distance and what amps i would have at the Summer house already from a spur...
     
    • Agree Agree x 7
    • Funny Funny x 3
    • Winner Winner x 1