Search the forum,

Discuss Summer house in the UK Electrical Forum area at ElectriciansForums.net

farqu01

DIY
Reaction score
9
Hi, looking for suggestions or indeed what you guys do when wiring in SWA to plastic house CUs.

gland swa to a Metal JB then connect from JB to CU?

Fit sub main like the wylex fused isolator using 25mm meter tails via henley blocks to keep supply out of house CU rcds?

fit gland plate/nut to plastic CU then.fit glanded cable to this then earth gland plate to cu earth bar? Use breaker on rcd side?

its a 30 meter run 10mm 3core SWA spare 40 and 45 amp breaker available in CU.

Just looking for ideas of what you guys do, cheers
 
Your details say "DIY" but in Scotland, so the Part P building requirements don't apply. The forum rules don't allow for advice that might be dangerous/illegal to follow, but you seem to be asking sane questions. Can you clarify your electrical skill/experience?

In terms of the actual question, it kind of depends on the use of the summer house and how much trouble power loss would cause. If you have a spare 40A MCB slot then it is easy to feed a small CU and feed sockets, lights, etc, but you will have poor selectivity between MCB/MCB(RCBO) due to both having the "instant" magnetic trip.

With SWA you could feed it via a fused-switch, sized as high as the SWA fault-clearing Zs will allow to get good selectivity, but ideally also 1.6 times smaller then the DNO fuse to ensure total selectivity with that. For example, if you have a 63A DNO fuse then a sub-main on 63/1.6 = 40A (closest) fuse cannot blow your DNO fuse no matter what.

But doing so means splitting your house CU tails, and that means you either have an isolator already or will need the DNO to pull the fuse to allow the work to take place.

For the SWA gland it can go in to plastic, but you need to use the banjo or an "Earthing nut" to properly bond the armour to the MET to allow fault clearing, even if 3 core so it has the CPC inside.

Unless you have some real experience in doing this I would say you should get in a professional. You see what the details are, discuss your options, and if acceptable do the cable install (or duct, so you can also run network cable along side it, etc) yourself.
 
Your details say "DIY" but in Scotland, so the Part P building requirements don't apply.
No, but it's common sense to do things properly and safely - Scottish volts are as dangerous as English ones.

The forum rules don't allow for advice that might be dangerous/illegal to follow, but you seem to be asking sane questions.
My first thought was that he's asking questions which aren't related either/ors -

gland swa to a Metal JB then connect from JB to CU?

Fit sub main like the wylex fused isolator using 25mm meter tails via henley blocks to keep supply out of house CU rcds?
Are not two different ways to "wire SWA to plastic house CUs".


Can you clarify your electrical skill/experience?
Good question - I'm concerned that he's picked up a few terms here and there but doesn't truly understand them. Can't help thinking that anybody really competent to do this work would know whether he wanted the summer house fed from the CU or not.

Then there's the T-word....


Unless you have some real experience in doing this I would say you should get in a professional. You see what the details are, discuss your options, and if acceptable do the cable install (or duct, so you can also run network cable along side it, etc) yourself.
plus_one.gif
 
Hi, thanks for the feed back.

Yes I come from an electrical back ground, mainly industrial, oil rigs/platforms. Mainly maintenance on LV/HVelectrical systems, power generation and instrumentation
Have done plenty of SWA glanding into motors,switchboards and various other apperatus etc.
Perhaps I did not word my original post in a coherant way. I do apologise for that, I did not expect to criticised for seeking information.

PC1966 has answered my question and I am going for the banjo. I just wanted to be 100% that this was fine to do.I thank you for that.

I will of course be more down with the lingo if I have further questions, after all this is what forums are for or atleast what I though they were for.

Have a nice day :)
 
I should add that if glanding to plastic you are much better to use an Earthing nut / piranha nut (instead of traditional banjo) as they lock to the threads and retain a good contact / no loosening without too high a compressive force for the plastic. These sort of things:
https://www.NoLinkingToThis/p/earthing-nut-2020-2-pack/77809

Just need a ring crimp terminal for the fixing screw to wire transition. Personally I would connect both ends (armour to CPC core/earth terminal) even if you would be OK for fault clearing on the armour alone (i.e. R1 + R2 of armour is enough to meet Zs when attached just at the source, not needing parallel CPC to bring down Rs at the load end), just gives that extra path for safety.
 
Last edited:
I should add that if glanding to plastic you are much better to use an Earthing nut / piranha nut (instead of traditional banjo) as they lock to the threads and retain a good contact / no loosening without too high a compressive force for the plastic. These sort of things:
https://www.NoLinkingToThis/p/earthing-nut-2020-2-pack/77809

Just need a ring crimp terminal for the fixing screw to wire transition. Personally I would connect both ends (armour to CPC core/earth terminal) even if you would be OK for fault clearing on the armour alone (i.e. R1 + R2 of armour is enough to meet Zs when attached just at the source, not needing parallel CPC to bring down Rs at the load end), just gives that extra path for safety.
Thanks for your advice PC 1966 it is appreciated

All the best ?
 

Reply to Summer house in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
706
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi guys I am taking on a job of supplying/wiring a summer house which is in the process of being built. Consumer unit has no spare ways so my...
Replies
23
Views
3K
I have a metal Hager sub CU, 10 way RCBO, installed in 2018 in an accessible attic space, this sub-CU being fed from another unit close to the...
Replies
11
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock