Discuss Surge protection/ark fault detection in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
30
Hi there just a few questions I have to do an install of a small ware house that was built in 2021 January (finished) client that is going into the warehouse specialises in laboratory. Now he has a lot of 3 phase machinery like mixers and small hoists which are all 3 phase the building adjacent to it he wants about 40 x sockets in there to be used as an office and testing station
Iam going to run swa etc for 3 phase and sockets in the office area now due to amendment 2 I know the surge protection will have to go in but will arc fault apply to this thank-you in advance (just out my time gaining knowledge as I go thanks )
 
Last edited by a moderator:
The regs state you must have afdd in the following :
• High risk residential buildings (HRRB)
• Houses in Multiple Occupation
• Purpose-built student accommodation
• Care homes

For all other there use is recommended
There may be additional requirements in a laboratory setting
 
As @newfutile said.

AFDD might be worth it if it is a place that has flammable materials, etc, so ask the client.

Other aspect you see in some laboratory situations is high leakage currents from lots of electronic stuff, again check with the client for end use. If they plan on having 13A sockets off a big UPS you would be better to hard-wire the UPS supply without RCD (or with 100mA delay, etc, if TT or other reasons for wanting that such as fire risk) and place a 30mA RCD on its output, otherwise no additional protection from the supply as if there is an earth fault the UPS keeps going!
 

Reply to Surge protection/ark fault detection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I was asked to go and take a look at a generator set up by a marquee company yesterday to do some testing. It was a brand new JCB 65QS with...
Replies
7
Views
2K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
2K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Hi All, I've joined today because I'm after some advice from people in the field about what requirements are necessary and what maybe considered a...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock