Client doesn’t want external cable . Shop with a three way mains incomer 9 m away . 2 flats fed on other feeds .So was going to run the 16mm SWA from the incomer in a low wall chase internally and run up the wall into a flush CU . So no RCD protection but earthed sheath . Do I have to sink it more than 50mm or is it mech protected anyway ?

thanks in advance !
 
No it will be fine. There is no specific depth to sink a cable except that if it is less than 50mm it may need additional rcd protection which in your case doesn't apply due to the construction of the cable.
 
There are 'safe ones' though. As long as the chase for the SWA is directly below the CU, and stays within the vertical boundaries of the CU, then it will be compliant
 
Try to fit a solid steel plate over the chase if you can that way some numpty will hopefully stop drilling with an SDS by the time they've hit the plate.
 
Try to fit a solid steel plate over the chase if you can that way some numpty will hopefully stop drilling with an SDS by the time they've hit the plate.
unless he's a kitchen fitter/plumber/builder/handyman.
 
Thanks for the replys . It has to run low level above the drainage pipework so cant get it into a safe zone until it gets to the vertical , so probably 2 m not in a prescribed safe zone . The worry is as pointed out some one spend 5 minutes with an SDS looking for a fixing and hits the mains . Not sure if steel plate that length would be cost effective . Think I will try and get the chase at 80mm and bury it below the 50mm min . Within the regs and would hope someone would notice if they hit it !
 
Thanks for the replys . It has to run low level above the drainage pipework so cant get it into a safe zone until it gets to the vertical , so probably 2 m not in a prescribed safe zone . The worry is as pointed out some one spend 5 minutes with an SDS looking for a fixing and hits the mains . Not sure if steel plate that length would be cost effective . Think I will try and get the chase at 80mm and bury it below the 50mm min . Within the regs and would hope someone would notice if they hit it !

Is the wall substantial enough to dig 80mm out of it?
 
is the drainage in the wall or surface? if surface you could box it in and the SWA inside the box as well.
 

Reply to SWA buried in wall to CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted...
Replies
20
Views
2K
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock