Hello all, was supposed to be running a bit of 6 mm swa along outside of building for a shed. My plan was just to clip it along wall above ground floor extension. Customer now wants me to just lay swa on top of fibre glass roof. They are saying they don’t want to see cable clipped to wall from back of garden. This does not seem right to me. I cannot find anything in regs to say no. Just wondered what people’s thoughts are?
 
Is there any regulation on 'securely fixing cables' ?

Is the swa creating a hazard being on the roof ?

Can't think of much else, I'm not familiar with bs7671
 
tell your customer that by doing that the cable is not secured. reg 522.8..4.. 05.
I think that's a misinterpretation of the regulations. The point of horizontal/vertical support is to avoid undue stresses to the mechanical properties of the conductors. A cable which is laid on something, end to end, is by nature actually supported along its entire length - it's no different to having that SWA buried in a trench or cables in conduit.

HOWEVER - what does come into play here is temperature. That cable is going to get roasting hot on a roof in the summer, and with fibreglass it's not going to have any radial dispersion at all. So the ambient temperature needs to be readjusted in the design calcs which might well mean that a larger conductor size is required or using xlpe @90+ ℃.

OP - have a read of App 4, 7.1

Goes without saying...... rough as dogs, even if it's 'legit'.
 
............HOWEVER - what does come into play here is temperature. That cable is going to get roasting hot on a roof in the summer, and with fibreglass it's not going to have any radial dispersion at all. So the ambient temperature needs to be readjusted in the design calcs which might well mean that a larger conductor size is required or using xlpe @90+ ℃.............
Maybe you could just tell them to reduce the load by a few Amps for the few days of summer..?
 
Is it suitably supported to prevent premature collapse in the event of a fire.
I think the water faeries would be more concerned being entangled in a few tons of collapsing roof that the few kilos of SWA on top of it.

Or is it a bit like the Covid cause of death? If there's unsupported cables within 28m of a dead water faerie then the cause of death is entanglement?
 
Say you'll do it but you'll have to attach cable tray to the roof with adhesives. See what they say then
IMG_20170408_110500.jpg
 
I was on a similar job years ago. Flat roof. We laid 2x2 slabs on the roof, then screwed the regular tray brackets to them.

Can’t remember now if it was swa or pyro we ran on the tray???

The roof in the OP may not be flat
 

Reply to Swa on top of fibre glass roof in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, Does any one know what kind of insulation resistance to expect for pink fibre wall/ceiling insulation? I'm trying to figure out if the...
Replies
13
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
889
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K
Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock