I'm just wondering if anyone knows of a product that can switch between 8kw loads?

The customer I have (a Deli) wants to add a 8kw pizza oven but only has a single phase supply and is already at capacity at 80 amps.

He has a industrial size oven and chicken rotisserie which totals around 8kw which is used during the day and the pizza oven would be used at night. I want a product that would switch between the 2 modes (day and night) and not able to all be turned on at once.

Cheers
 
For dedicated switching between two 8kW appliances, the OP could go 40A CPD to a 40A changeover switch, which will probably be smaller and cheaper. I read this as the one 8kW appliance (be it day or night appliance) plus "everything else" takes the load up to around 80A
 
Good luck with that. Make sure you detail the cert. Pretty likely after you've done they'll find a way to run both together with a nail in the fuse to stop it blowing.
 
a digital time clock and use it to control a contactor,
The contactor would power one or the other,
the time clock sets when that is
easy as !
next problem ?
That's very restrictive - sooner or later they will want to use the pizza oven during the day, encouraging a botch.

The IEC60309 idea could work, however as the load is just north of 32A, you would have to use the much larger 63A variants, which aren't the easiest to couple and uncouple for the layman. Personally I wouldn't be comfortable with someone potentially struggling with connectors in a food prep area with hot equipment closeby.

Either a 40A changeover switch or 3xIEC60309 connectors, plus cabling, assembly and testing will probably be in the region of £200.
 
It really is very simple. A changeover switch is the best thing for the job. Will look neat, professional and is readily available.

I am sure this is a non-issue but usually changeover switches have two supply terminals and one load terminal. In this setup there is one supply and two loads. It may be worth checking technical sheets to ensure they will work as required. As I said I am pretty certain it will be fine but will be worth a check.
 
many moons ago there was a thread about someone having 2 showers but wanted a changeover switch for them so they both can't come on at the same time. Someone posted one.
You could use something similar. Switching high loads.
 

Reply to Switching high loads so as not to go over 80 amps. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
935
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
632
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
701
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock