Discuss SY cable for distribution circuits and final circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
2
Hi all,

Just a question relating to SY cable and the use of SY cable. My boss his carrying out a EICR for a industrial premise and coming across a lot of SY cable. These cables are used for final circuits and distribution circuits. I know that BS7671 list SY cable as non - standard cables and are covered by the Germany VDE regulations, but would you code this as a code and if so what code and what regulation would it go under ? Would like more information in SY and similar types of cables.

Thanks
 
Well the OSG lists them as not suitable for final circuits. However it hasn't stopped a lot of persons using it for ring final circuits (have to say that as someone is watching and they get touchy if you don't use the proper name) etc. I think manufacturers don't classify it as suitable for such circuits as you describe. But on control circuits perfectly normal for use. I personally would use common sense and consider environment, loads and state of the cable before I wouldn't code it anything if it looked fine and environmental factors were suitable and suitably rated what is the problem. I think they do not fare well in damp/wet environments and the plastic coating may not be happy with certain chemicals. It is a controversial topic.
 
I come across it a lot (although not as sub mains) when doing EICRs, if it's in good condition and appears to be suitable for what it's supplying, then I wouldn't note it as being wrong, in fact we did a new installation where it was specified to use SY as final circuits to supply server cabinets.
 
We use a lot as finals to power rectifiers etc. As long as it's suitable for the environment and the voltage rating I don't have a problem with it.
 
Also seeing more YY cable being used in metal trunking for distribution supplies (probably as it's easier to bend )
 
The braid is designed as a screen on SY, if it is suitably earthed but not used as the Earth then just list a comment of not recognised under our cable standards, on the assumption we are talking LV.
 
Just a question relating to SY cable and the use of SY cable. My boss his carrying out a EICR for a industrial premise and coming across a lot of SY cable. These cables are used for final circuits and distribution circuits. I know that BS7671 list SY cable as non - standard cables and are covered by the Germany VDE regulations, but would you code this as a code and if so what code and what regulation would it go under ? Would like more information in SY and similar types of cables.

We use SY cable. As long as its used properly then I don't see a problem.
Where does BS7671 says SY cable is 'non-standard' ? I can't find it.
 
We use SY cable. As long as its used properly then I don't see a problem.
Where does BS7671 says SY cable is 'non-standard' ? I can't find it.

It doesn't specify SY or any other cable type, however it does specify the standards to which cable must be approved either British standards, harmonised European standards or international standards.
The problem is that SY is made to a German national standard (VDE), this is not a harmonised standard or an international standard and so technically does not comply.

Also manufacturers data sometimes specifies that this cable is not suitable for installation work, connection to public LV mains supplies or similar.
 
Where are the volt drop, current carrying capacity and derating factors to be found on this cable. Even claims of manufacture to a VDE standard seem sketchy
 

Reply to SY cable for distribution circuits and final circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, Currently undertaking an EICR on a factory, we have came across an 4 core SWA and 4 Core SY which have been split in the DB to serve two...
Replies
14
Views
3K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Hi all, Interested in the groups interpretation of BS7671 with regards to the used of SY & YY cables. We have a commercial installation where we...
Replies
8
Views
2K
Came into work today with a fairly urgent requirement to install an instant hot water handwash unit in a small commercial kitchenette/servery -...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock