Discuss SY Cable? Thoughts? in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
30
Morning all

I've recently been introduced to SY cable through work. I've had a look for more information on the web as I wanted to check ratings, uses etc. but I'm getting a lot of mixed information... many people say they use it but many others are saying that it doesn't comply with BS7671.

Apparently it is widely used on the continent for both control and power. I wondered if anyone could enlighten me on it's use in the UK.

I tried to search the forums for info but couldn't see relevant threads...

Thanks in advance

L
 
I can’t speak for all manufacturers but Elandcables website says that it is not suitable for fixed wiring for compliance with bs7671.
Take a look at their site.
 
This subject has interested me. What did they change?

They put a comment in that it was not suitable for fixed installations, but I cant find it now.... Strange.

Olflex state
upload_2018-11-9_9-2-2.png

I'll keep searching
 
Belden state:
upload_2018-11-9_9-12-33.png

The below is pinched from @Massive1 post above:

'VDE 0250'
The VDE Institute is a national and internationally accredited institution in the field of testing and certification of electrotechnical devices, components and systems. (VDE stands for Verband der Elektrotechnik, Elektronik und Informationstechnik)

VDE publish a series of standards covering, among other things, various cable types. However, simply quoting the term, 'VDE 0250' is meaningless because it is not a specification and the ‘0250’ is just one part of a complete standard number. In order to be meaningful, the full standard number must be quoted. For example, the German NYM type of cable is defined in VDE 0250-204:2000.

The full VDE standard to which these cables might conform is unclear.

VDE standards are German national standards. They are neither Harmonised European (EN) nor International (IEC) standards. Therefore their use under BS 7671 is not automatic and they would be subject to the required engineering assessment regarding safety, etc.

NAPIT understands that the VDE Institute has issued certification to a small number of cable manufacturers for some SY, CY, and YY cables and that this certification is based on individual cable manufacturer specifications which are confidential to both VDE and the manufacturer. As these specifications have not been published, we are unable to determine which material and construction specifications or tests have been applied. Consequently, authoritive literature is not available to assist in making engineering judgements.
 
Morning all

I've recently been introduced to SY cable through work. I've had a look for more information on the web as I wanted to check ratings, uses etc. but I'm getting a lot of mixed information... many people say they use it but many others are saying that it doesn't comply with BS7671.

Apparently it is widely used on the continent for both control and power. I wondered if anyone could enlighten me on it's use in the UK.

I tried to search the forums for info but couldn't see relevant threads...

Thanks in advance

L

Out of interest mate. Why use SY cable? Why not use NYY-J cable?
NYY-J cable is cheaper and you don't need a special gland, so the gland is cheaper as well.
 
Cheers, I think the powers that be want the extra mechanical protection though...

Can you please clarify what the cable will be used for.
Is it for the mains power for machinery or V.S.D. to motor connections....
 
Can you please clarify what the cable will be used for.
Is it for the mains power for machinery or V.S.D. to motor connections....
They are using it to supply power to a water heater, five core SY L1, L2, L3, N and PE but they want it screened as well. I believe that they need to control the water temp quite accurately so I assume this is why they require the screen.
 
This has come up before.. What is the right thing to do? On some machines you can't rely upon RCD protection so you kind of need a cable with mechanical protection built in, and earth sheathed in case it is damaged/crushed.

Always feels to me like an unfair choice, to either downgrade real-world safety in order meet the regs, or follow common sense and risk criticism for it.
 
SY and machinery, depends on the environmental influences, SY usually requires other IP and mechanical protections around machinery as it is not suitable to the oils, coolants etc commonly used, also it shouldn't really be bought as a mechanically enhanced protected cable, this is a screening and originally design for screening purposes, it should have additional mechanical protection if used in areas where it may be subject to damage etc.
 
SY and machinery, depends on the environmental influences, SY usually requires other IP and mechanical protections around machinery as it is not suitable to the oils, coolants etc commonly used, also it shouldn't really be bought as a mechanically enhanced protected cable, this is a screening and originally design for screening purposes, it should have additional mechanical protection if used in areas where it may be subject to damage etc.

This biggest problem if you decide to use the braid which you shouldn't, as part of a means for ADS is assessing the braids capability of carrying fault current.

Fair points.

The thing is, the braid is a useful last defence if the cable is damaged (unnoticed) and then someone touches it. In general, it's also pretty tough stuff. Designed for screening, but designed to be extra tough too.

Even 'fixed' machines get moved away from walls for servicing etc. Damage can occur at anytime and for me, SY feels like a good choice. I accept the braid can't be relied on solely, but one day it might be in the right place to save a nasty incident. Just feels right to earth the surface of exposed cable if it's possible to do so.
 
Last edited:
A few points to note:-

SY cable does not comply to British Standards in using it you will have:-
A- understand why it does not comply.
B- document its use and why you believe it is suitable for your installation.

The use of this cable in the industry brought it big concerns and was clearly been used for purposes it was never designed for or was suitable for.
If you have it on or around machinery where it may come into contact with the normal oils, greases, coolants etc used then it should not be used.
If it is subject to possible damage then it should not be chosen in the mindset that it is a armoured flex, it is not it is a screened flex which can afford some kinds of damage a standard flex couldn't but also it is prone to damage where other flexes would be resistant IE UV damage, outer sheath is softer than standard pvc environmental covering and it has low resistance to chemicals and oils.

I conclude this cable should not even be in our industry, it is mi-sold, misused and has forced the regulatory bodies to step it and express its use does not conform to our recognised standards.

I have a pet hate of this cable because of the amount of times I have seen the result of its poor application, I have in 2 decades found several times that damaged cable has made the sheath live and in some cases given uses shocks simply because of misuse and the wrong applications of its use.

I would say if you have routine machine movement for maintenance and cleaning then wire it with a suitable HO7RN-F a cable designed for the purpose of most industrial environments and put it on a plug and socket arrangement so it can be disconnected, I have done this for many decades and never had issues, if you find you are then the operators/employees need educating and taught how to clean and service the machines safely.
 

Reply to SY Cable? Thoughts? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, Interested in the groups interpretation of BS7671 with regards to the used of SY & YY cables. We have a commercial installation where we...
Replies
8
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
664
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock