Discuss Tails in cavity wall in the UK Electrical Forum area at ElectriciansForums.net

I’ve used it but you can drill through it with an sds quite easily so I’m in two minds whether it compliant for mechanical protection

Hi - agree it’s possible to drill through. I’m thinking that 522.6.204 (iv) doesn’t require the protection be drill proof, just prevent penetration by nails and screws. I’m relying on the British manufacturer who recommends it for this job. Maybe I’m too trusting?

In the end it would be better if the tails were not there in the first place.

5A960CCF-61DB-4690-BEE2-E1C3945488AD.jpeg
 
I would agree that running tails in a cavity or any other cable is bad practice for a number of reasons including:

1) Possible unseen damage to cables pulled through the cavity over the hidden portion.

2) De-rating factors should insulation be present or added to the cavity at a later date.

3) The cavity (if it hasn't already been filled with crap already from the bricky) is a potential chimney. So should there be an issue with the installation and an electrical fire starts in the cavity then the fire integrity of the building could be compromised.

4) Even before things like Part P and the good old competent person schemes existed I believe that the old NICEIC Technical Handbook used to specifically frown on the practise of any cables being installed in cavities and it would have been considered poor workmanship if the practise was used.

So for what it's worth if the metre cabinet isn’t on the front elevation of the house and there is not neat and tidy way of routing the tails indoors, (taking account of requirements for suitable earthed mechanical protection etc. if buried) then I would go down the route of external SWA clipped direct on the exterior wall and through wall directly into the CU.
 
The problem is even externally its in a narrow passage shared between two houses leading to gardens which again is not ideal. Added on to that DNO's don't like any customer equipment in their boxes. Its one of those between a rock and a hard place because of the alterations made. I think the best solution is to try and feed some kind of copex even if just pvc 32mm, at least it gives it some protection from future insulation or falling debris.

Remembering there is a utility box on the outside and consumer unit on the inside there is no real risk of anyone wanting to drill through the wall in that position.

Given its only a 3 bed semi and using 25mm tails de-rating will not be an issue.
 
If the cut out is 100A then 25mm tails are mandatory irrespective of load (taking into account diversity).
No cables are allowed in a cavity other than meter tails 'which must pass directly through i.e. perpendicular to the wall'
So the choices are you either run up the outside then go straight through the wall, or through the wall then up the inside (both with suitable protection for the 'up' bit)
And if the total length will end up more than 3m, then you need to provide overload protection to that run.
Those are the rules, the customer has to be told to like it or lump it.
 
Hi - agree it’s possible to drill through. I’m thinking that 522.6.204 (iv) doesn’t require the protection be drill proof, just prevent penetration by nails and screws. I’m relying on the British manufacturer who recommends it for this job. Maybe I’m too trusting?

In the end it would be better if the tails were not there in the first place.

View attachment 49504
Electrical safety first recommends minimum 3mm steel for this application
 
No cables are allowed in a cavity other than meter tails 'which must pass directly through i.e. perpendicular to the wall'
So the choices are you either run up the outside then go straight through the wall,

Not sure what you mean here - any cable can pass directly through a wall.
 
Not sure what you mean here - any cable can pass directly through a wall.

Yes, but not run in a cavity. You're right, any cable can pass perpendicularly through the cavity, it's preferred that meter tails do so also, however they are the only cables that may deviate e.g. enter the cavity then go up slightly, then exit, recognising that we don't live in an ideal world.
 
OSG 2.2.3.1 Consumer's Tails, 2nd paragraph. '...and the minimum cable size should be 25mm"
That is not a regulation, mearly guidance going to a default csa for fuses that are rated at 100 amps.
There’s no such regulation preventing you using say 16 mm tails as the fuse could be rated lower than 100 amps
 

Reply to Tails in cavity wall in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I would like to hide the cable to an EV charger. The consumer unit, meter cabinet and charger would all be on the same wall. About 5 metres from...
Replies
19
Views
2K
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
403
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
744
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock