hi tuf is not classed as flexible. flex does not go big enough, xlpe I don't think is a flexible cable either.
 
just looking up h07rnf looks like for 32a ill need a 6mm 3c but there is also (H)07RC4N8-F which offers more protection or am i going OTT for a flexible lead?
 
Section 717 mobile or transportable units -
717.52 Wiring systems
717.52.1 Where the supply to the unit is by means of a plug and socket outlet, flexible cables in accordance with H07RN-F (BS EN 50525-2-21), or cables of equivalent design, shall be used for connecting the unit to the supply.
 
Section 717 mobile or transportable units -
717.52 Wiring systems
717.52.1 Where the supply to the unit is by means of a plug and socket outlet, flexible cables in accordance with H07RN-F (BS EN 50525-2-21), or cables of equivalent design, shall be used for connecting the unit to the supply.
Oh, thank you for spending the time to find that for me. so I have a get out of jail free card if I use the cable and they damage it. I'm usually always overly cautious with these things and thinking what if !!
 
I have a get out of jail free card if I use the cable and they damage it.
Really H07RN-F is pretty tough, if you need more intrinsic protection then it is really SWA and that is not suited for anything that moves more than very occasionally.

Keeping the flex out of harm's way is the best plan, so attached to tray or in some duct, maybe an overhead hawser if clearance for vehicles, etc, allows it, etc, if you can. However, many temporary sites have nothing to helps with that and are quite brutal in how they treat cables :(
 

Reply to Temporary building supplies again in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I'd appreciate the wisdom of the find minds here regarding this job. Yes, I've drifted into Wales again.... An extension is being planned as...
Replies
4
Views
924
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
707
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock