Evening all,

Does anyone now what the correct arrangement for a temp building supply is these days. I am just about to start first fix a new build and am going to have to provide temp supply . In the past I have put in an Earth rod, tails onto a switch fuse/dp isolator and out into a little board with rcd as main switch. Dno can then connect to the switch fuse /dp isolator etc. One of my colleagues suggested that they now would
Like an s type rcd before the consumer unit as it is a TT. Does anyone know what they like these days as I have tried to get in contact with power networks but I am still waiting for a reply
Many thanks
 
up front RCD 100ma S type, then into consumer unit 30ma RCD protection at that point, earth rod & tested with results would be good.
might get away with 30ma rcd unit at board without the 100ma but they might not connect.
3 phase definitely wont connect you without the 100ma trip
 
Is it a temporary building on a construction site or a construction site temporary supply? Not entirely clear from the thread title.
There's a difference. One comes under section 7, one does not.
 

Reply to Temporary building supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
875
What are peoples opinion's on this, pair of big old semi-detached houses (85 and 87) converted into apartments, dont think its a HMO although it...
Replies
1
Views
252
Evening, I've been asked to install a supply to a sprinkler system in a new installation that must be separate to the building electrical...
Replies
2
Views
571
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock